    2kW AC compressor high current.



    Hi all,
    what is a rough resistance on PSC 1Ph motor of about 2kW input power. I have 0.5ohm and 1.5ohm roughly. Is this in the ballpark? I compressor is pulling big amps (2x max running), it is a rotary type, starts OK but I am suspecting that the compressor is sticky. The only thing that doesnt make sense with that diagnosis is that a sticky compressor wouldn't start easily right? should i change out the capacitor?
    thank you!



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: 2kW AC compressor high current.

    Quote Originally Posted by Harrison View Post
    Hi all,
    what is a rough resistance on PSC 1Ph motor of about 2kW input power. I have 0.5ohm and 1.5ohm roughly. Is this in the ballpark? I compressor is pulling big amps (2x max running), it is a rotary type, starts OK but I am suspecting that the compressor is sticky. The only thing that doesnt make sense with that diagnosis is that a sticky compressor wouldn't start easily right? should i change out the capacitor?
    thank you!
    what is you ampere and voltage?

  3. #3
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: 2kW AC compressor high current.

    240V so that makes running amps 8.5A. I have been thinking a bit more, if a bad capacitor was causing the extra current (over double running amps, 21A or so) surely the cap would be getting seriously hot, no?
    thoughts??

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 2kW AC compressor high current.

    You need to check the existing cap with a test meter to see if it is out of range.

    If you were to swap the cap and it worked ok, maybe the cap was bad, maybe it would have run ok that time anyway.
    The cap could be bad and the system could have another fault, a test meter will help you determine whats going on.

    Jon

  5. #5
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: 2kW AC compressor high current.

    Ok Cap may be bad what do people think about the resistances in the motor windings. I know there are some reference books around with tech data for common compressors, where does one get these??
    thank you

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Maximum Starting Current
    By weeliang82 in forum Air Conditioning
    Replies: 4
    Last Post: 29-04-2010, 04:15 AM
  3. Scroll compressor current
    By Scott Buker in forum New Technologies
    Replies: 2
    Last Post: 02-10-2009, 11:54 PM
  4. York Reciprocating Chiller - %Motor Current
    By subdude in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2009, 05:49 PM
  5. Motor Current Fault York RecipPak YCUZ880E8
    By iaHVACguy in forum Trouble Shooting
    Replies: 0
    Last Post: 23-07-2009, 02:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •