    Some expert advice required



    Need some expert opinion on effect in refrigeration system working with R134a and synthetic oil contaminated with forane-141b.
    One of our customer had run a centrifugal chiller operating with R134a and synthetic oil – 46 grade, after charging fresh refrigerant. On few minutes, the oil pressure dropped drastically. On evaluation it was found that the oil viscosity had dropped down by almost 50%. On testing, the refrigerant was found to be contaminated with forane-141b.
    Can you please suggest any possible effects of forane-141b on a synthetic oil and effect of R134a & forane-141b mixture?



  2. #2
    Space Shifter's Avatar
    Space Shifter Guest

    Re: Some expert advice required

    sounds to me like the system wasnt flushed properly to remove all the old oil...

  3. #3
    Join Date
    Feb 2009
    Location
    bruges
    Age
    45
    Posts
    42
    Rep Power
    0

    Re: Some expert advice required

    Quote Originally Posted by Dheeraj View Post
    Need some expert opinion on effect in refrigeration system working with R134a and synthetic oil contaminated with forane-141b.
    One of our customer had run a centrifugal chiller operating with R134a and synthetic oil – 46 grade, after charging fresh refrigerant. On few minutes, the oil pressure dropped drastically. On evaluation it was found that the oil viscosity had dropped down by almost 50%. On testing, the refrigerant was found to be contaminated with forane-141b.
    Can you please suggest any possible effects of forane-141b on a synthetic oil and effect of R134a & forane-141b mixture?

    whas the unit charged enough to start with ... (R134a)

  4. #4
    Join Date
    Jul 2010
    Location
    New Zealand
    Posts
    11
    Rep Power
    0

    Re: Some expert advice required

    Quote Originally Posted by Dheeraj View Post
    Need some expert opinion on effect in refrigeration system working with R134a and synthetic oil contaminated with forane-141b.
    One of our customer had run a centrifugal chiller operating with R134a and synthetic oil – 46 grade, after charging fresh refrigerant. On few minutes, the oil pressure dropped drastically. On evaluation it was found that the oil viscosity had dropped down by almost 50%. On testing, the refrigerant was found to be contaminated with forane-141b.
    Can you please suggest any possible effects of forane-141b on a synthetic oil and effect of R134a & forane-141b mixture?
    get the feeling there is more to this than you are letting on...........WHY was 141B in there?, WHY wasn't it removed ? how long was the vacuum ????

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Some expert advice required

    R141b is a flushing agent. Did the system have a burn out or was it flooded with water?

Similar Threads

  1. Advice required Air / Water heat pump systems
    By oddjob1607 in forum Heat Pumps
    Replies: 8
    Last Post: 13-12-2010, 07:48 PM
  2. refrigeration theory - advice required
    By solas in forum Fundamentals
    Replies: 4
    Last Post: 21-01-2010, 02:28 AM
  3. peugeot expert ...... advice
    By thebigcheese in forum Chit Chat & Service Stories
    Replies: 6
    Last Post: 27-08-2009, 11:50 PM
  4. Mitsubishi Heavy Industries FDC2501 tech advice required
    By aeaves in forum Air Conditioning
    Replies: 1
    Last Post: 20-04-2009, 08:44 AM
  5. Advice required
    By abbasi in forum Fundamentals
    Replies: 3
    Last Post: 01-10-2006, 03:26 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •