Results 1 to 12 of 12
Thread: subcooling
    Mar 2009
    32
    subcooling
    how do you measure subcooling
    Feb 2008
    505
    Re: subcooling
    you convert the head pressure reading to tempreture then messure the liquid line tempreture the dif between the saturated tempreture and actual temp is subcooling
    Spencer ma.
    108
    Re: subcooling
    read Refrigeration 101: by Gary
    Aug 2009
    New Zealand
    2,554
    Re: subcooling
    Quote Originally Posted by martinw58 View Post
    This not quite correct, actual sub-cooling you need to measure the liquid pressure (and convert to a saturated temperature) and measure the actual liquid temperature, the difference between the temps is the actual level of sub cooling. Sorry for being so perdantick, as this is one of my pet subjects.
    Aug 2007
    Sydney
    1,083
    Re: subcooling
    Yes oldtimer
    madfridgie is very correct as usual. A few more tips - If no access point is available at outlet of cond or liquid line allow for pressuredrop through condenser of more than about 5psi. There is nothing like an accurate measurement so get your self a superheat calculation kit like yellow jacket (ritchie) and measure the refrigerant temp and pressure directly. Even if you have to pump down the unit and weld in a schrouder port anywhere on the liquid line.
    Feb 2007
    newcastle but now carlisle
    195
    Re: subcooling
    Quote Originally Posted by Tesla View Post
    Yes oldtimer
    hes asking about subcooling not superheat
    Aug 2007
    Sydney
    1,083
    Re: subcooling
    Cool tony--1
    But just check it out first - the superheat calc kit measures sub cooling directly as well as superheat.
    Split Croatia
    6,151
    Re: subcooling
    Cool tony--1
    That we call humor, my friend.
    karas's Avatar
    karas Guest
    Re: subcooling
    sir how can i know if the subcooling measure are correct compare to the superheat of evaporator
    karas's Avatar
    karas Guest
    Re: subcooling
    Quote Originally Posted by tony--1 View Post
    sorry sir im just new im quite thinking the balances of both measurement ,like in multi stage.
    Aug 2009
    New Zealand
    2,554
    Re: subcooling
    Quote Originally Posted by karas View Post
    Kamusta (tagalog not to good)
    Sub cooling has no direct relationship to evaporator superheat. If you have no sub cooling at the expansion valve, then you are likely to have a mix of liquid and vapour. The mix will will reduce the mass flow through the valve, causing the evaporator to be starved (not enough liquid) if the evap is starved then you will have high superheat.
    I hope this is what you meant?
    Total Racer's Avatar
    Total Racer Guest
    Red face Re: subcooling
    The others have measuring subcooling correct, but system needs to be fully loaded, all cond. fans running. May have to manipulate low ambient controls if cold enough outside.
  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
  3. Subcooling
    By samisonfire in forum Technical Discussions
    Last Post: 21-04-2010, 09:23 PM
  4. Subcooling
    By terryw in forum Supermarket Refrigeration
    Last Post: 07-03-2007, 09:53 AM
  5. Subcooling & Refrigerants
    By US Iceman in forum Fundamentals
    Last Post: 29-04-2006, 02:59 AM