    chiller tank



    hi,

    Im lynark, i just want to ask how to compute the number of coils you need to used in a chiller tank. Because i have seen a water tank with so many copper tube loop together thats why i wonder how the installer or designer computed for that. assuming you already have the Cooling capacity needed.

    thank you



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: chiller tank

    Heat Loss per Foot/Metre should help.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    Trial and error, depends on too many variables.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: chiller tank

    hi peter_1

    so it means their is no proper computation? just by years of experience.


    hi brian_uk

    can you give some a brief sample?


    actually i'm more on designer of coldroom coldstorage. Now i want to try deeper application of refrigeration system. i want to start on this basic one. So any help is really appreciated

  5. #5
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Q=h*A*(tp-tw)
    h - surface heat transfer coefficient
    A - surface area of pipes
    tp - surface temperature of pipes
    tw - surrounding water temperature
    You must know surface heat transfer coefficient (pipe/water), it's the most difficult.
    Try to find ASHRAE's articles "HEAT TRANSFER" and "LIQUID COOLERS".
    In some places will have to think ...

  6. #6
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Surface heat transfer coefficient (h) depends on many factors: density, viscosity, thermal conductivity of fluid, geometrical dimensions of clad body and etc. Also coefficient depends on velocity of fluid relatively the clad body. For natural covection of fluid surface heat transfer coefficient is:
    115 - 700 kW/(m^2*C)
    For forced convection water surface heat transfer coefficient is:
    115 - 11500 kW/(m^2*C).
    There aren't general theory of finding this coefficient but there are some theories for special cases.
    In some places will have to think ...

  7. #7
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: chiller tank

    Quote Originally Posted by Aik View Post
    Surface heat transfer coefficient (h) depends on many factors: density, viscosity, thermal conductivity of fluid, geometrical dimensions of clad body and etc. Also coefficient depends on velocity of fluid relatively the clad body. For natural covection of fluid surface heat transfer coefficient is:
    115 - 700 kW/(m^2*C)
    For forced convection water surface heat transfer coefficient is:
    115 - 11500 kW/(m^2*C).
    There aren't general theory of finding this coefficient but there are some theories for special cases.


    Hi aik,

    thanks for the info. So the Q is the computed heat load needed for the pipe? So by that i can find the Surface area of pipes? And how many loops needed from the header?


    thank you

    lynark

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    We did a test some weeks ago for a heatpump, a coil 3/8 " of 50 ft submerged in water at 12°C, Te + 1°C, R134a for standstill water gives extracts 475 W.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Quote Originally Posted by lynark View Post
    Hi aik,

    thanks for the info. So the Q is the computed heat load needed for the pipe? So by that i can find the Surface area of pipes? And how many loops needed from the header?


    thank you

    lynark
    Q - is the heat [W];
    A - is the surface area of pipes [m^2];
    A=Pi*D*l
    Pi=3.14
    D - external diametr of pipe [m]
    l - lenth of pipe [m]
    The most hard poroblem is how to calculate h...
    In some places will have to think ...

  10. #10
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    For a single pipe situated in fluid:
    Nu=h*D/k - Nusselt number
    h - surface heat transfer coefficient [W/(m^2*K]
    D- diameter of pipe [m]
    k – thermal conductivity of fluid [W/(m*K)]

    Re= V*D/ν - Reynolds number
    V - velocity of fluid [m/s]
    ν- kinematic viscosity factor [m^2/s]

    Pr=μ*c/k - Prandtl number
    μ – dynamic viscosity factor of fluid [Pa*s]
    c – specific heat of fluid [J/(kg*K)]


    Index "f" cover to temperature of fluid, "p" cover to temperature of pipe.
    Attached Images Attached Images
    In some places will have to think ...

  11. #11
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    For corridor disposition of pipes:
    Attached Images Attached Images
    • File Type: jpg 1.JPG (63.2 KB, 16 views)
    • File Type: jpg 2.JPG (18.2 KB, 13 views)
    In some places will have to think ...

  12. #12
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    For as on a chess-board disposition of pipes:
    Attached Images Attached Images
    • File Type: jpg 3.JPG (42.8 KB, 8 views)
    • File Type: jpg 4.JPG (10.9 KB, 4 views)
    In some places will have to think ...

  13. #13
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    You must determine Nu, than determine h, after determine A and l.
    If angle between fluid flux and pipe differ than 90, than h must be multiplited by corresponding factor.
    Attached Images Attached Images
    • File Type: jpg 5.JPG (11.1 KB, 18 views)
    In some places will have to think ...

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    Aik, can you translate/calculate these formulas to see if they match my practical test?
    Last edited by Peter_1; 30-05-2010 at 08:48 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Quote Originally Posted by Peter_1 View Post
    Aik, can you translate/calculate these formulas to see if they match my practical test?
    I must know velocity of water and angle between water flux and pipe in your case. Also I must know disposition of pipes: single pipe, corridor or chess-board disposition...
    In some places will have to think ...

  16. #16
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: chiller tank

    hi aik, peter_1

    here's the details of the chiller tank i have seen.


    tank dimension: 4 ft x 8 ft x 4 ft depth
    water temp in the tank should be 10 C
    water ( stand still ) no circulation


    thank you

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    What do you want to cool with the water?
    We need desired temperature in and out and required flow.
    What compressor you want to use?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Quote Originally Posted by Peter_1 View Post
    We did a test some weeks ago for a heatpump, a coil 3/8 " of 50 ft submerged in water at 12°C, Te + 1°C, R134a for standstill water gives extracts 475 W.
    Aik, can you translate/calculate these formulas to see if they match my practical test?
    Peter_1, can you give data of velocity and angle, or may be can you give draft (domensions and connections) of your tank and volume flow of water. Then I'll try to calculate...
    In some places will have to think ...

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    We submerged a standard 3/8 spiraled coil of 50 ft in water, diameter of spirals 35 cm (1.15 ft) and 2 cm (0.8 inch) from each other.
    No water flow, only agitation of the water with a small air blower at the bottom of the tank.
    Thanks
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Quote Originally Posted by Peter_1 View Post
    We submerged a standard 3/8 spiraled coil of 50 ft in water, diameter of spirals 35 cm (1.15 ft) and 2 cm (0.8 inch) from each other.
    No water flow, only agitation of the water with a small air blower at the bottom of the tank.
    Thanks
    It's natural convection:
    In some places will have to think ...

  21. #21
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Formula is:
    Attached Images Attached Images
    In some places will have to think ...

  22. #22
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    I don't fully understand the calculation, but I do it and result is true...
    Attached Files Attached Files
    In some places will have to think ...

  23. #23
    sanwar's Avatar
    sanwar Guest

    Re: chiller tank

    Dear Freind,
    Could you please provide me "1 year hvac preventive maintenance schedule in ms-word formate

    Thanks,
    Sanwar

  24. #24
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    Sanwar, post his in a new thread, not hijacking this one.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  25. #25
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    Aik, I'm impressed with your result as long as you haven't changed numbers to fit the result.
    What about a 1/2" and a 5/8 " of 50 ft, same conditions?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  26. #26
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Quote Originally Posted by Peter_1 View Post
    Aik, I'm impressed with your result as long as you haven't changed numbers to fit the result.
    What about a 1/2" and a 5/8 " of 50 ft, same conditions?
    Peter_1, if you change diameter of pipe "D" you'll get result (capacity) for new pipe with the same conditions. Also you may change length "L" of the pipe...
    In some places will have to think ...

  27. #27
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    Aik, where can I find all the numbers you inserted in your formula?
    Your formula was a question which was asked many times here on RE. If we're sure about it, we then don't have to test it in real life the next time.

    What about a 3/8 coil buried in the ground? Problem will be that you will not find the right numbers for 'ground' which can be anything.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  28. #28
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: chiller tank

    Aik, If I give in the correct diameter for a 3/8 pipe which is 0.009525 and not 0.09525, then I get 80 W instead of 454 W So something is wrong with the calculation
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  29. #29
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    Quote Originally Posted by Peter_1 View Post
    Aik, If I give in the correct diameter for a 3/8 pipe which is 0.009525 and not 0.09525, then I get 80 W instead of 454 W So something is wrong with the calculation
    You are right, I found mistake in my calculation...Today I'll try to explane all calculations
    In some places will have to think ...

  30. #30
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller tank

    What about a 3/8 coil buried in the ground? Problem will be that you will not find the right numbers for 'ground' which can be anything.
    In ground there isn't convection because the ground is solid. Therefore thise calculation don't used for ground.

    Aik, If I give in the correct diameter for a 3/8 pipe which is 0.009525 and not 0.09525, then I get 80 W instead of 454 W So something is wrong with the calculation
    I have reform the calculation...
    Peter_1, really I gave coefficient for limited space from other method of calculating, but I suppose it's correct... Also I gave operation factors at temperatures 0 and 10 C, because I don't know its at temperatures of 1 and 12 C. If you give thise operation factors at needed temperatures you'll get more precisely result.
    Attached Files Attached Files
    In some places will have to think ...

  31. #31
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: chiller tank

    hi aik and peter_1,

    I think i'm a little lost with your conversation. and thinking this is only a basic one

Similar Threads

  1. Chiller expansion tank.
    By Helper monkey in forum Fundamentals
    Replies: 4
    Last Post: 16-11-2009, 02:27 AM
  2. Beer Chiller Malfunction
    By glennk in forum Trouble Shooting
    Replies: 14
    Last Post: 05-08-2009, 12:36 AM
  3. Co2 Tank refrigeration system
    By Prashant Kumar in forum CO2
    Replies: 7
    Last Post: 24-04-2009, 07:55 PM
  4. How an expansion tank works?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 25-07-2008, 02:25 PM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 07:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •