Thread: york chiller problems
-
27-05-2010, 05:28 AM #1
york chiller problems
hi guys am new to posting on this site but long time guess you could say fan as I have used this site on a few occasions to solve issues but now I need to ask a question
I have a york ycwj999xx chiller with three j style comps mounted and stage three feeps displaying error code "motor current" I have checked in coming lines voltage and amps the comp is pulling also I have checked contactor and contacts (contactors are new) and also checked the current transformer which seems to be ok, so I am at a loss of what to check next ????? the comp giving me the problems is new only changed 3 months ago but the same error code came up just before the old comp crapped itself (have asked the mob who took it away what they found with it but no reply
also on the same chiller (stage2) when loading up comp sounds terrible like piston is hitting top of head and when loaded up it shakes the whole chiller so bad the pcb,s and tb's are coming loose.
any help given would be great, thanks guys and R.E love the site, now I am registered cant wait to hopefully help some one one day with a problem
thanks again Jase in space
-
27-05-2010, 06:20 AM #2
Re: york chiller problems
Your motor protector serially wired with H.P. Switch.so if you have any H.P SWITCH issue display will show motor protection.so check the h.p. switch continuity and motor protector.
moideen-Dubai
-
27-05-2010, 08:26 PM #3
Re: york chiller problems
Hi:
it would seem like you have 2 problems electrical ,and mechanichal.
you should check wiring ,of the wires going to the current transformer ,you could messure the actull curent by inserting a amp meter in series.
then i would check for liquid slugging ,or internal mechanichal failure.THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
28-05-2010, 07:12 AM #4
Re: york chiller problems
you could messure the actull curent by inserting a amp meter in series.
Hi Goshen.
I am not sure about that one my friend on most York units you cannot make a direct comparison.
Between the current drawn display and the measured (Say with a clamp meter) Value.
Try it on a working unit and you will see what i mean.
Jase.
A 3 month old machine with either issue is someones warranty Problem.
Time to call someone back!
Grizzly
-
28-05-2010, 01:45 PM #5
-
29-05-2010, 12:03 AM #6
Re: york chiller problems
Hi Jase
Doe's the compressor 'run on' slightly when stopped ?
If your electrics check out ok & the compressor supplier side steps any waranty the next step could be to remove the heads & carry out a valve gear inspection.
If the vibration is worse with a particular set of pistons when they load-up, start with that head first..
Is the compressor new or a reman of the old one ?Last edited by Gingerair; 29-05-2010 at 12:06 AM.
-
29-05-2010, 12:38 AM #7
Re: york chiller problems
Three things can cuase motor current trips on these,
1. Current tranformers
2. H.P
3. Motor protection module
you say you have checked the cts , try and change with the other compressor to be sure , also check auxillary contacts on the contactors.
Check the motor protection module and thermistors
Check the H.P switch ( not the transducer )
Make sure transtition of contactors is also ok
Hope this will help
-
31-05-2010, 12:11 AM #8
Re: york chiller problems
Thanks for all the reply guys, I have changed ct's with other stages and fault still occurs, have tonged all three phases on trouble comp and nothing wrong there. Thermistors and motor protection module are ok too. The only fault that really stands out is oil pressure is little low, but oil pressure fault would not come up as " motor current" fault. Few of you guys said to look at hp at time of fault disc press was apx 1740kpa and has transducers.... (btw system is r22)
-
01-06-2010, 10:40 AM #9
Re: york chiller problems
Hi Jase
Just re-read your original post..
Stage 3)
What Moideen & Intercas are saying is check your HP switch (not transdeucer) for being faulty, not just tripping.
As Intercas said the items listed are the ones that can cause your type of fault.
Also check for loose plugs.
Have you meggered the compressor windings to check if they're ok ?
Is the oil in a good condition, is it showing any acidity ?
Why was it re-built, was the original cause of any failure identified ?
The low oil pressure is not a good sign, how confident are you that they've carried out a proper reman ??..
Stage 2)
Can you pump this circuit down, will it then hold a head of pressure ?
Stripdown & carry out a top-end inspection..
Lots of questions i know..
Let us know what you find..
-
13-12-2010, 09:25 PM #10
Re: york chiller problems
Could anyone help???????
I need a fault code book or manual for a York Clima Roca
SOH0901
S/n 0404905412010
Have spoken York and Johnson Cotrols with dismay
Cheers Alex
-
22-01-2011, 04:16 PM #11
Re: york chiller problems
Jase in Space did u check the programmed motor current values.
Setrite
A group of Donkey's Led by a Lion can defeat a group of Lion's led by a Donkey
-
02-02-2011, 07:56 PM #12
Re: york chiller problems
Send me your e-mail , probabily I can help you
Z
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
york chiller ylcs control logic problems
By koolkatz in forum Trouble ShootingReplies: 2Last Post: 04-12-2009, 11:59 AM -
York chiller problems
By robert ames 195 in forum Trouble ShootingReplies: 1Last Post: 12-05-2009, 09:59 PM -
York Liquid Chiller problems.
By kanodogg in forum CommercialReplies: 4Last Post: 09-05-2008, 09:16 PM -
problems with york yaa c chiller
By paulwild in forum CommercialReplies: 4Last Post: 21-08-2007, 08:20 PM