    york chiller problems



    hi guys am new to posting on this site but long time guess you could say fan as I have used this site on a few occasions to solve issues but now I need to ask a question
    I have a york ycwj999xx chiller with three j style comps mounted and stage three feeps displaying error code "motor current" I have checked in coming lines voltage and amps the comp is pulling also I have checked contactor and contacts (contactors are new) and also checked the current transformer which seems to be ok, so I am at a loss of what to check next ????? the comp giving me the problems is new only changed 3 months ago but the same error code came up just before the old comp crapped itself (have asked the mob who took it away what they found with it but no reply
    also on the same chiller (stage2) when loading up comp sounds terrible like piston is hitting top of head and when loaded up it shakes the whole chiller so bad the pcb,s and tb's are coming loose.
    any help given would be great, thanks guys and R.E love the site, now I am registered cant wait to hopefully help some one one day with a problem
    thanks again Jase in space



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: york chiller problems

    Your motor protector serially wired with H.P. Switch.so if you have any H.P SWITCH issue display will show motor protection.so check the h.p. switch continuity and motor protector.
    moideen-Dubai

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: york chiller problems

    Quote Originally Posted by jase in space View Post
    hi guys am new to posting on this site but long time guess you could say fan as I have used this site on a few occasions to solve issues but now I need to ask a question
    I have a york ycwj999xx chiller with three j style comps mounted and stage three feeps displaying error code "motor current" I have checked in coming lines voltage and amps the comp is pulling also I have checked contactor and contacts (contactors are new) and also checked the current transformer which seems to be ok, so I am at a loss of what to check next ????? the comp giving me the problems is new only changed 3 months ago but the same error code came up just before the old comp crapped itself (have asked the mob who took it away what they found with it but no reply
    also on the same chiller (stage2) when loading up comp sounds terrible like piston is hitting top of head and when loaded up it shakes the whole chiller so bad the pcb,s and tb's are coming loose.
    any help given would be great, thanks guys and R.E love the site, now I am registered cant wait to hopefully help some one one day with a problem
    thanks again Jase in space
    Hi:
    it would seem like you have 2 problems electrical ,and mechanichal.
    you should check wiring ,of the wires going to the current transformer ,you could messure the actull curent by inserting a amp meter in series.
    then i would check for liquid slugging ,or internal mechanichal failure.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: york chiller problems

    you could messure the actull curent by inserting a amp meter in series.

    Hi Goshen.
    I am not sure about that one my friend on most York units you cannot make a direct comparison.
    Between the current drawn display and the measured (Say with a clamp meter) Value.
    Try it on a working unit and you will see what i mean.
    Jase.
    A 3 month old machine with either issue is someones warranty Problem.
    Time to call someone back!
    Grizzly

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: york chiller problems

    Quote Originally Posted by Grizzly View Post
    Hi Goshen.
    I am not sure about that one my friend on most York units you cannot make a direct comparison.
    Between the current drawn display and the measured (Say with a clamp meter) Value.
    Try it on a working unit and you will see what i mean.
    Jase.
    A 3 month old machine with either issue is someones warranty Problem.
    Time to call someone back!
    Grizzly
    Hi Grizzly
    i stand corrected ,you can only messure the current on the old units with the external seperate ct's,
    on the new ones this is impossible !
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  6. #6
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    16

    Re: york chiller problems

    Hi Jase

    Doe's the compressor 'run on' slightly when stopped ?

    If your electrics check out ok & the compressor supplier side steps any waranty the next step could be to remove the heads & carry out a valve gear inspection.

    If the vibration is worse with a particular set of pistons when they load-up, start with that head first..

    Is the compressor new or a reman of the old one ?
    Last edited by Gingerair; 29-05-2010 at 12:06 AM.

  7. #7
    Join Date
    Jun 2006
    Location
    Australia
    Posts
    8
    Rep Power
    0

    Re: york chiller problems

    Three things can cuase motor current trips on these,

    1. Current tranformers
    2. H.P
    3. Motor protection module

    you say you have checked the cts , try and change with the other compressor to be sure , also check auxillary contacts on the contactors.

    Check the motor protection module and thermistors
    Check the H.P switch ( not the transducer )

    Make sure transtition of contactors is also ok

    Hope this will help

  8. #8
    jase in space's Avatar
    jase in space Guest

    Re: york chiller problems

    Thanks for all the reply guys, I have changed ct's with other stages and fault still occurs, have tonged all three phases on trouble comp and nothing wrong there. Thermistors and motor protection module are ok too. The only fault that really stands out is oil pressure is little low, but oil pressure fault would not come up as " motor current" fault. Few of you guys said to look at hp at time of fault disc press was apx 1740kpa and has transducers.... (btw system is r22)

  9. #9
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    16

    Re: york chiller problems

    Hi Jase

    Just re-read your original post..

    Stage 3)
    What Moideen & Intercas are saying is check your HP switch (not transdeucer) for being faulty, not just tripping.
    As Intercas said the items listed are the ones that can cause your type of fault.
    Also check for loose plugs.
    Have you meggered the compressor windings to check if they're ok ?
    Is the oil in a good condition, is it showing any acidity ?
    Why was it re-built, was the original cause of any failure identified ?
    The low oil pressure is not a good sign, how confident are you that they've carried out a proper reman ??..

    Stage 2)
    Can you pump this circuit down, will it then hold a head of pressure ?
    Stripdown & carry out a top-end inspection..

    Lots of questions i know..
    Let us know what you find..

  10. #10
    Join Date
    Feb 2009
    Location
    NOTTINGHAM
    Posts
    9
    Rep Power
    0

    Re: york chiller problems

    Could anyone help???????

    I need a fault code book or manual for a York Clima Roca
    SOH0901

    S/n 0404905412010

    Have spoken York and Johnson Cotrols with dismay

    Cheers Alex

  11. #11
    Join Date
    Jul 2001
    Location
    Good bay
    Posts
    50
    Rep Power
    24

    Re: york chiller problems

    Jase in Space did u check the programmed motor current values.
    Setrite

    A group of Donkey's Led by a Lion can defeat a group of Lion's led by a Donkey

  12. #12
    Join Date
    Nov 2010
    Location
    Romania
    Posts
    10
    Rep Power
    0

    Re: york chiller problems

    Send me your e-mail , probabily I can help you

    Z

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. york chiller ylcs control logic problems
    By koolkatz in forum Trouble Shooting
    Replies: 2
    Last Post: 04-12-2009, 12:59 PM
  3. York chiller problems
    By robert ames 195 in forum Trouble Shooting
    Replies: 1
    Last Post: 12-05-2009, 09:59 PM
  4. York Liquid Chiller problems.
    By kanodogg in forum Commercial
    Replies: 4
    Last Post: 09-05-2008, 09:16 PM
  5. problems with york yaa c chiller
    By paulwild in forum Commercial
    Replies: 4
    Last Post: 21-08-2007, 08:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •