    Prestcold
    Hi there! Does anyone know the KW of a prestcold R750/0138 ?? I have 19 amps but i am going to use a soft start (experiment!!) and i must know the kw...
    The label on the compressor unfortunately is erased from the years... Thanks anyway!!
    3,853
    Re: Prestcold
    I think thats a 7.5HP compressor, is it a big cast iron three cylinder 3ph compressor?
    May 2010
    greece
    5
    Re: Prestcold
    Yes that right!! Thanks !!!
    Feb 2008
    502
    21
    Re: Prestcold
    7.5 hp is 5.56 kw
    May 2010
    greece
    5
    Re: Prestcold
    To be exact i do not know if it has 3 cylinders...the head is big though...you maybe right but i am not sure! Thanks anyway.
    May 2010
    greece
    5
    Re: Prestcold
    I can convert Kw to hp but i do not know either.... I think that it is 7,5 hp too, if i compare suction-discharge-amps...etc .Thank to all
    Aug 2009
    new zealand
    57
    44
    Re: Prestcold
    The first numbers indicate the horsepower and the last figures (0138) the displacement, the R indicates the body type.
    Aug 2009
    New Zealand
    2,554
    26
    Re: Prestcold
    you can not size your electrical on the nominal hp (which actually only rates to power drawn at a fixed condition) in this case 7.5Hp, you must use your amps for sizing a soft starter, which 19amps max sounds about right 400v 3phase 50hz which would be close to 9.5kw
    Auckland
    74
    3,357
    38
    Re: Prestcold
    Well explained MF. The LRA is the main thing to bare in mind.
  1. Prestcold Semi-hermetic
    By Iceberg1138 in forum Tools and Calculators
    Last Post: 19-02-2010, 02:26 AM
  2. Replies: 0
    Last Post: 09-08-2009, 03:30 AM
  3. Relay for Prestcold K202D
    By colingwatkins in forum Electrical
    Last Post: 25-06-2009, 10:19 AM
  4. Prestcold K100 & K150
    By colicool in forum Technical Discussions
    Last Post: 21-07-2008, 09:30 AM
  5. Identification of a Prestcold
    By vinic in forum Fundamentals
    Last Post: 06-01-2005, 02:23 AM