    I am retrofitting an older propane based system to have a much higher suction pressure and flow (but same condensing temp). We've bought a new condenser and replaced the motor for the higher power requirements, but am wondering about compressor relief valve sizing. The compressor is a P8WB recip machine and the relief valve is a Mycom but I have no idea on orifice or capacity. Any suggestions? How do I resize this orifice - am I required to?



  2. #2
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Mycom Relief Valve

    If the relief valve was originally sized for propane according to the B-52 code (Canadian) there is no need to change it when you change the operating condition of the compressor. If the valve is over years old, it should be changed according to code requirements.
    Attached Files Attached Files

  3. #3
    Join Date
    Aug 2008
    Location
    Canada
    Posts
    6
    Rep Power
    0

    Re: Mycom Relief Valve

    charlie: This is great! Thanks. How many years is it before I require replacement? You were typing and missed the # of years.

  4. #4
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Mycom Relief Valve

    Sorry, 5 years

  5. #5
    Join Date
    Jan 2008
    Location
    West Coast British Columbia
    Age
    51
    Posts
    106
    Rep Power
    17

    Re: Mycom Relief Valve

    Charlie also note that you can size the capacity of the valve on the lowest capacity of the machine if there is a means of force unloading at high pressure situations. Since you are using a P8WB machine you can use something like the CP1 controller from Mycom to force the compressor to be a 2 cylinder when pressure approaches relief pressure.

    This can make a very large difference on size of valve and the line from it.
    Refrigeration is not just cool, it is my life.

Similar Threads

  1. Replies: 3
    Last Post: 26-08-2009, 09:37 AM
  2. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  3. Mycom relief valve issue?
    By Mojjee in forum Industrial
    Replies: 32
    Last Post: 15-05-2009, 03:26 AM
  4. Oversize Relief Valve
    By Dacosta in forum NH3
    Replies: 1
    Last Post: 05-09-2008, 11:35 AM
  5. Carbo Cooler relief valve
    By flasah in forum NH3
    Replies: 2
    Last Post: 24-06-2006, 09:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •