    Cool Our new aquarium - can also be used as a refrigeration system



    G'day,

    We've had a few systems with moisture in them from time to time, sometimes containing free water in things like water chillers where theres been a leak under the water level.... But I think the one we had today took the cake. It was full (literally, full) to the brim with water after a split plate heat exchanger caused the refrigeration system to dump all the gas out into a pressurised water gallery... which meant once the gas pressure stopped coming out, the water came with 50psi behind it.

    I took a few quick videos while we were working on it. At first there was surprise at 'a' liter of water that came out. But once we got a bit more serious it was apparent how much more there was. We have taken 40+ liters out so far, and theres still a possibility the condensor has free water trapped in it too.

    (sorry for the lack of clickable links, but apparently I'm a spambot because I havent made 15 posts so I'm not to be trusted with the mighty power of a URL yet) EDIT: Cancel that..... I have enough posts to magically turn them into links now. Thank goodness, I appear to have passed the Turing test.

    http://www.youtube.com/watch?v=rnKVkLW8RZU
    Amazement at the spray of water

    http://www.youtube.com/watch?v=HdVYncELhCw
    Amazement at the constant trickle of water

    http://www.youtube.com/watch?v=7a4rpUFbiFU
    Thinking maybe theres quite a lot of water in this system

    http://www.youtube.com/watch?v=vTgaLexBUbI
    KNOWING theres a lot of water in this system

    http://www.youtube.com/watch?v=puETwh5sIqc
    Bloody obvious reason for lots of water in the system

    http://www.youtube.com/watch?v=cRksMyzb3nQ
    Proof you cant keep a good compressor down
    (Ended up pulling -30 inches on the gauge at ~12A and held off perfectly, though did use about 6 vac pump oil changes, 4L of solvent and 10L of compressor oil to do it)

    Anyone have any jobs that ended up full of water like this one? We reguarly see wet systems but this was a little ridiculous. I was expecting to see a goldfish in the sight glass!
    Last edited by The Red Krawler; 27-05-2010 at 11:36 AM.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Our new aquarium - can also be used as a refrigeration system

    Hi Red,

    I've had an icebuilder split its coil and fill up the refrigerant circuit with water, resulting in most of the u bends on the condenser bursting! We scrapped the system.

    On another milk tank we had the coil go, it had a big maneurop comp on it and when i undid the suction valve all the oil came out as it was sitting on top of the water! We repaired the coil and got the system dried out and it was still running 10 years later.

    Good luck with your system


    Jon

  3. #3
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Our new aquarium - can also be used as a refrigeration system

    had an aircondition system on a passenger ship where they tried to pump down the freshwater chiller to change the filterdriers and froze it solid and broke 6 pipes.

    the water circuit was closed and had 6 bars of pressure, first they dumped a metric ton of R-22 into the freshwaterpipes, then they proceeded to fill the entire chiller and compressor unit with water.

    had to drill lots of holes to drain everything and flush with ofn, then ran the vacuum pump for 2 months.

    Luckily the water that entered the compressor unit displaced the oil up into the compressor and preserved it
    -Cheers-

    Tycho

  4. #4
    Join Date
    Sep 2007
    Location
    Brisbane, Australia
    Posts
    44
    Rep Power
    0

    Re: Our new aquarium - can also be used as a refrigeration system

    Sounds like you guys had this happen on a bigger scale than what we did, though to a similiar extent. I dont know what sort of internal volume the refrigeration circuit has on this machine but I dont think theres much pipework that isnt full of water in here.

    We've gone through 2 x 'C' sized dry nitrogen bottles so far, and somewhere near 8 vaccum pump oil changes. Everything is being done via copper lines instead of gauge lines now to speed up the process, but getting free water to move is hard.

    On the plus side, the compressor saw 800 microns today which is promising, and with a few strategic cuts at low points on the rest of the system we've moved on the vast majority of the free water. Mostly vapour left now!

    Its going to be a bit of a wait for the evaporator as noone in Australia carries anything in this configuration so we have to see whats going to be the best option - a custom build, modifying all the pipework or waiting for an OEM part to be delivered (6 - 8 weeks MINIMUM! Urgh).

  5. #5
    cjay's Avatar
    cjay Guest

    Re: Our new aquarium - can also be used as a refrigeration system

    Quote Originally Posted by monkey spanners View Post
    Hi Red,

    I've had an icebuilder split its coil and fill up the refrigerant circuit with water, resulting in most of the u bends on the condenser bursting! We scrapped the system.

    On another milk tank we had the coil go, it had a big maneurop comp on it and when i undid the suction valve all the oil came out as it was sitting on top of the water! We repaired the coil and got the system dried out and it was still running 10 years later.

    Good luck with your system


    Jon
    had ship system once that filled up with water from hold coils, job started with getting abucket of water out of crankcase, ended up sailing with vessel for two weeks too keep system running

  6. #6
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: Our new aquarium - can also be used as a refrigeration system

    Hi Red Krawler
    Have you thought of using a water trap in line before your vac pump. This is a device that contains dry ice and the water vapour condenses and freezes on the cold surface and wont enter your vac pump. Wont dry your system any quicker but will save you some vac pump oil changes. The BPHE looks about the same size as used in Multistack chillers. You could try Leo at Kelvinair, he may have something in stock to help you out. PM if you need any help.

  7. #7
    Join Date
    Jul 2010
    Location
    South coast nsw
    Age
    41
    Posts
    9
    Rep Power
    0

    Re: Our new aquarium - can also be used as a refrigeration system

    Gday Red,
    Narooma pool heater (APAC unit), heater exchanger split dumped her gas and completly filled with pool water. Good stuff.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Our new aquarium - can also be used as a refrigeration system

    Plenty of jobs like that. The last one was a 120HP screw compressor chiller with a broken shell and tube condenser. Water up to the rim. Compressor rusted from inside. All scrapped.

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. High Liquid Line Temperature
    By airefresco in forum Commercial
    Replies: 37
    Last Post: 11-02-2009, 04:36 PM
  4. Refrigeration system simulation and optimization
    By autt in forum System Optimization
    Replies: 7
    Last Post: 05-12-2008, 02:59 PM
  5. Thermal Efficiency of Refrigeration System
    By hussain316 in forum Refrigeration Books
    Replies: 5
    Last Post: 31-07-2007, 08:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •