    Replacement Condenser Fan Motor Sizing



    Hi all,

    I'd like to get your thoughts on replacing a worn out condenser fan motor with a slightly more powerful one.

    The unit has a 6-pole, 1/8-hp motor, but those are expensive and hard to find. The motor is labeled 1,100 RPM.

    I have a 1/4-hp condenser fan motor I would like to use. This motor is also a 6-pole but is labeled 1,075 RPM. Since a 6-pole motor has a synchronous speed of 1,200 RPM, it can't go over that. So, in the worst-case scenario, the fan would be turning 9% faster with the new motor. I would think anywhere between 1,075 and 1,200 RPM should be acceptable.

    I'm not too worried about the possible increased current requirement. The motor is connected to the same contactor that switches the compressor, so it looks beefy enough to cope with an extra amp or two.

    Does anyone see a reason why I shouldn't replace the 1/8-hp motor with the 1/4-hp one?

    Thanks!



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Replacement Condenser Fan Motor Sizing

    If the fan remains the same, there is no reason at all worrying about the increased motor's power ; as to the decrease in rotational speed - it is negligeble 2,27%!

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Replacement Condenser Fan Motor Sizing

    The speed is irrelevant, the cfm is important.

  4. #4
    DrChill's Avatar
    DrChill Guest

    Re: Replacement Condenser Fan Motor Sizing

    Thanks for your help. My old motor finally seized, and I had to install the new one. It seems to work fine. It only draws 1.2 of the 1.7 A is is specified to draw at full power.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Replacement Condenser Fan Motor Sizing

    Check difference between air in and out temperature, if it is 8-10K your fan moves enough air.

  6. #6
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Replacement Condenser Fan Motor Sizing

    Quote Originally Posted by DrChill View Post
    Hi all,

    I'd like to get your thoughts on replacing a worn out condenser fan motor with a slightly more powerful one.

    The unit has a 6-pole, 1/8-hp motor, but those are expensive and hard to find. The motor is labeled 1,100 RPM.

    I have a 1/4-hp condenser fan motor I would like to use. This motor is also a 6-pole but is labeled 1,075 RPM. Since a 6-pole motor has a synchronous speed of 1,200 RPM, it can't go over that. So, in the worst-case scenario, the fan would be turning 9% faster with the new motor. I would think anywhere between 1,075 and 1,200 RPM should be acceptable.

    I'm not too worried about the possible increased current requirement. The motor is connected to the same contactor that switches the compressor, so it looks beefy enough to cope with an extra amp or two.

    Does anyone see a reason why I shouldn't replace the 1/8-hp motor with the 1/4-hp one?

    Thanks!

    I can't see you having any real problems.

    Manufacturers and designers try to make out that the way the
    condensing unit is put together is critical to the performance of the system.

    In reality the condensing unit is capable of taking many of the compressors in the
    companies range. It keeps costs down. So for most applications the cond is oversized
    anyway and it is only critical on the largest of compressors in the range.


    Just beware that if the fan is oversized it might be too effiecient in the winter
    and drop the head preasure too low..

    taz

    .

  7. #7
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: Replacement Condenser Fan Motor Sizing

    No problem we have as far as you increase motor power or rpm inturn increases CFM and forced co0nvection will be greater. We have done this many times and have decreased condenser area also by calculating proper heat rejection.
    No wonder it worked fine
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  8. #8
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Replacement Condenser Fan Motor Sizing

    No problem, more advantages in replacing a higher motor input power, as long as you don't deviate too much with the existing design requirements especially the airflow CFM.
    The 1,075 rpm is the motor nominal full load speed while the 1200 rpm is only the theoretical maximum speed the motor can operate. In actual operation, your motor will run at approx. 1,075 to 1150 rpm.
    <"No one is so smart, they just stay with problems longer and use their imagination">

  9. #9
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: Replacement Condenser Fan Motor Sizing

    The 1/4 is twice the size of the 1/8. That makes it significantly oversized. That would be similar to replacing a 1/4 with a 1/2.

    A common side effect of an oversized condenser fan motor is a excessive motor hum (noise).

  10. #10
    Join Date
    Aug 2009
    Location
    UNITED STATES
    Age
    65
    Posts
    19
    Rep Power
    0

    Re: Replacement Condenser Fan Motor Sizing

    Check the load amps on the 1/4 hp motor, if the amps are considerablely lower, than the unused hp will turn into heat energy and shut the motor from the over load protector.

Similar Threads

  1. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  2. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  3. Condenser Temperature. HOW TO model it in 3D?
    By ruzfactor in forum Fundamentals
    Replies: 6
    Last Post: 07-09-2009, 10:57 AM
  4. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  5. Plate Heat Exchagers - Condenser
    By Billy Ray in forum Technical Discussions
    Replies: 9
    Last Post: 11-05-2008, 06:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •