Thread: saturated pressure of 134a
23-05-2010, 06:19 AM #1
I have a cold room, required temp+3.evaporator sensor clamped on eva.centre coil. Refrigerant is r134a. evap.temperator shows 1c.room temp 10c.then td is ok.As convert the 1c saturation temp to pressure, should be get 44 psig. but gauge shows 15 psig. Anybody can clear
Moideen-Dubai
23-05-2010, 07:07 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: saturated pressure of 134a
Either your temp sensor is inaccurate or influenced with surrounding air flow or you have high superheat at that place or your pressure gauge is not showing correct pressure.
I bet on that probe is not insulated from surrounding air.
23-05-2010, 01:10 PM #3
23-05-2010, 01:53 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Not necessarily, what if we have restriction?
That is why we need full readings:
Evap air in temp
Evap air out temp
Low side pressure or saturation temp
Suction line temp at evap outlet
Cond air in temp
Cond air out temp
High side pressure or saturation temp
Liquid line temp at receiver or condenser outlet
23-05-2010, 10:18 PM #5
You should not be working on refrigeration equipment alone.
With the information provided it is impossible to diagnose the problem, in future look at readings on all listed above and this may point you in the right direction.
24-05-2010, 05:32 AM #6
Even Einstein Asked Questions
24-05-2010, 01:02 PM #7
thanks your replay.now getting required temp+3,so i dont have tension.there is no txv,discharge pressure access.my question was only saturated pressure-temp variation.
Max low side pressure in R404A system
By Wilade in forum Technical DiscussionsReplies: 8Last Post: 25-08-2009, 09:23 PM -
About liuid line pressure drop.
By wilsoncheung in forum Technical SpeculationsReplies: 15Last Post: 16-03-2009, 11:34 AM -
Vapour Pressure
By Stev in forum FundamentalsReplies: 7Last Post: 18-03-2008, 09:48 AM -
High Deferential Oil Pressure Alarm
By NNNNNN in forum Trouble ShootingReplies: 27Last Post: 24-12-2007, 01:06 PM -
Log p/h diagram
By Peter_1 in forum FundamentalsReplies: 5Last Post: 09-01-2007, 02:37 PM