    Question saturated pressure of 134a



    I have a cold room, required temp+3.evaporator sensor clamped on eva.centre coil. Refrigerant is r134a. evap.temperator shows 1c.room temp 10c.then td is ok.As convert the 1c saturation temp to pressure, should be get 44 psig. but gauge shows 15 psig. Anybody can clear
    Moideen-Dubai



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: saturated pressure of 134a

    Either your temp sensor is inaccurate or influenced with surrounding air flow or you have high superheat at that place or your pressure gauge is not showing correct pressure.
    I bet on that probe is not insulated from surrounding air.

  3. #3
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Question Re: saturated pressure of 134a

    Quote Originally Posted by nike123 View Post
    Either your temp sensor is inaccurate or influenced with surrounding air flow or you have high superheat at that place or your pressure gauge is not showing correct pressure.
    I bet on that probe is not insulated from surrounding air.
    according to suction pressure(15 psig) evap.temp is -25c.then why does get the room temp 10c.it should be -16c.
    moideen

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: saturated pressure of 134a

    Quote Originally Posted by moideen View Post
    according to suction pressure(15 psig) evap.temp is -25c.then why does get the room temp 10c.it should be -16c.


    moideen
    Not necessarily, what if we have restriction?

    That is why we need full readings:
    Evap air in temp
    Evap air out temp
    Low side pressure or saturation temp
    Suction line temp at evap outlet

    Cond air in temp
    Cond air out temp
    High side pressure or saturation temp
    Liquid line temp at receiver or condenser outlet

  5. #5
    Join Date
    Aug 2009
    Location
    new zealand
    Age
    57
    Posts
    44
    Rep Power
    0

    Re: saturated pressure of 134a

    You should not be working on refrigeration equipment alone.

    With the information provided it is impossible to diagnose the problem, in future look at readings on all listed above and this may point you in the right direction.

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: saturated pressure of 134a

    Quote Originally Posted by moideen View Post
    according to suction pressure(15 psig) evap.temp is -25c.then why does get the room temp 10c.it should be -16c.
    moideen
    If this was always true then life would be so much easier .

    Check the parameters which Nike123 mentioned. Probably you don't get the required capacity out of the evaporator.
    might be : wrong TEV, incorrectly adjusted TEV, pre-expansion in the liquid line .....

    Cheers
    Even Einstein Asked Questions

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: saturated pressure of 134a

    thanks your replay.now getting required temp+3,so i dont have tension.there is no txv,discharge pressure access.my question was only saturated pressure-temp variation.

Similar Threads

  1. Max low side pressure in R404A system
    By Wilade in forum Technical Discussions
    Replies: 8
    Last Post: 25-08-2009, 09:23 PM
  2. About liuid line pressure drop.
    By wilsoncheung in forum Technical Speculations
    Replies: 15
    Last Post: 16-03-2009, 11:34 AM
  3. Vapour Pressure
    By Stev in forum Fundamentals
    Replies: 7
    Last Post: 18-03-2008, 09:48 AM
  4. High Deferential Oil Pressure Alarm
    By NNNNNN in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2007, 01:06 PM
  5. Log p/h diagram
    By Peter_1 in forum Fundamentals
    Replies: 5
    Last Post: 09-01-2007, 02:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •