Results 1 to 13 of 13
    May 2010
    India
    49
    9
    Help Required for Selecting Thermal Expansion Valve.
    Dear Friends
    I require help for selecting a thermal Expansion Valve for Copeland Copelamatic Semi Hermetic Compressor Model No: LAHA- 032E -TAD-220. Its for a -20 deg cold storage ,the size of the cold storage is 10 feet length X 8 feet width X 8 feet Height.
    I require a compatible Thermal Expansion Valve and the refrigerant is R -22.
    Can any one suggest me the compatible Thermal Expansion Valve.
    Thanks.
    Split Croatia
    57
    6,151
    36
    Re: Help Required for Selecting Thermal Expansion Valve.
    That compressor is for R404A and R507 refrigerants.
    Nov 2009
    Minsk, Belarus
    171
    15
    What is capacity, condensing and evaporating temperature?
    In some places will have to think ...
    Split Croatia
    57
    6,151
    36
    For R404a:
    Danfoss TES 2 with orifice 03
    Emerson TCLE-2-SZ
    May 2010
    India
    49
    9
    Quote Originally Posted by Aik View Post
    Dear Sir
    Following parameters are available with us.
    ReFrigerant : R 22
    Evaporating Temp = -26C
    Condensing Temp = + 50 - 55 deg. C
    Sub-cooling Temp = Not Known
    System Capacity @ above conditions : Not exactly known. Its a -20 deg c cold storage and it has got Semihermatic Copeland Copelamatic Compressor Model No. LAHA - 032E - TAD - 220. The system is almost 12-14 years old.
    Please help us to find a compatible thermal expansion valve.
    Split Croatia
    57
    6,151
    36
    Do you have old expansion valve? What is his make and model number?
    What is evaporator make and model number?
    At this conditions:
    Te=-26°C
    Tc=50°C
    subcooling 6K
    evaporator superheat 4K
    total superheat 20K
    your compressor have about 3,4 kW cooling capacity with R22 refrigerant.
    Your expansion valve could be Danfoss TEX 2 with orifice 02 or 03 which depend on size of evaporator.
    Buy both orifice and try smaller one at first.
    Selection of TXV should be done according to evaporator capacity.
    Feb 2008
    Las Vegas, NV
    67
    330
    NIKE is correct that the LAHA-032E-TAD compressor is not rated for low temp R22.
    But the LAHA-031A-TAD (different motor) is rated for low temp R-22.
    In the past when R502 was going away many manufacturers (ie: Hussmann) tested compressors and used them outside Copelands ratings. I suspect this is the case being that R22 was the replacement choice at the time.
    With that said, my official SWAG calculation of the LAHA-032E-TAD capacity using R22 would be:
    12,260 btuh @ -15F (-26C) SST
    90F (32C) ambient
    460-3-50 Hertz
    I suggest you use a 1.5 nominal ton balance port TEV
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com
    Aug 2009
    new zealand
    57
    44
    Has the original valve failed ? Has this system allways run on r22 , What is loading on room is it not possible to run a refrigerant suited to the compressor
    Running this compressor on r22 at the suggested condensing with no additional subcooling to compressor you will be running with excessive discharge pressures , this will break down the oil over a period off time forming carbon on the discharge valves and other detrimental effects in the long term.
    Compressors have operation parameters for good reason.
    Aug 2009
    new zealand
    57
    44
    Sorry above should read excessive discharge tempreatures not pressures.
    Nov 2009
    Minsk, Belarus
    171
    15
    At this conditions:
    Te=-26°C
    Tc=50°C
    subcooling 6K
    total superheat 20K
    In general I agree... Nike where do you get subcooling 6K?
    Evaporating Temp = -26C.....
    Its a -20 deg c cold storage ....
    Difference between evaporator and storage temperatures (6K) is to small for mechanical TXV... For stable work TXV minimum difference is 7K...
    Split Croatia
    57
    6,151
    36
    http://www.refrigeration-engineer.co...&postcount=160
    May 2010
    India
    49
    9
    Now I will be using a new Copeland Copelamatic Semi Hermetic Compressor , Model No : LA40-030E . with R 404a refrigerant , The product catalog of Copeland Says at condenser temp: +55 Deg C ant Evaporating Temp: - 20 Deg C , the compressor has cooling capacity of 3.45 Kw.
    Can any one help to find a suitable TXV Preferably Danfoss.
    11,025
    Quote Originally Posted by Allied01 View Post
    <snip>, the compressor has cooling capacity of 3.45 Kw.
    Try your refrigeration parts supplier, they should have one.
  1. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Last Post: 10-09-2008, 01:25 AM
  2. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Last Post: 22-06-2008, 12:29 PM
  3. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Last Post: 08-06-2008, 06:52 PM
  4. Thermal Expansion Valve Info
    By bernard in forum Supermarket Refrigeration
    Last Post: 14-09-2007, 11:51 PM
  5. help required in locating expansion valve power head
    By Tejbir Singh in forum Trouble Shooting
    Last Post: 10-12-2004, 02:38 PM