19-05-2010, 12:54 PM #1
screw compressor CSH 75
Hello
I have a little problem with this compressor.
the controler shows high discharge temperature.
What can be possible failures
-
19-05-2010, 09:14 PM #2
Re: screw compressor CSH 75
What are the operating conditions? what is the refrigerant?
-
20-05-2010, 07:03 AM #3
Re: screw compressor CSH 75
Hi Mikseidis.
There could be many reasons for your High pressure Fault.
If the tranducer is reading correctly.
The speed at which you observe the HP rise from start-up would be a good indicator.
Also is this a stand alone system or 1 of several. etc.
In no particular order
lack of HP cooling, Cond. water / air?
overcharged? (unlikely unless you have adjusted the charge).
Air in the system?
chocked liquid strainer?
Condenser scaled or dirty?
Moisture in the system?
Faulty Expansion Valve (closed)?
For example!
Cheers Grizzly.
For a better answer give us more info!
-
20-05-2010, 07:01 PM #4
Re: screw compressor CSH 75
What AC/Refrigeration system you are using?,also the refrigerant?..,more info pls..
<"No one is so smart, they just stay with problems longer and use their imagination">
Similar Threads
-
VSD on screw machines
By Mike Hopkins in forum New TechnologiesReplies: 14Last Post: 20-02-2011, 12:10 AM -
R22 - R417 (RetroFit) Screw set A.C
By Chris_Atlantic in forum Trouble ShootingReplies: 3Last Post: 23-04-2010, 06:53 PM -
Compressors - screw or reciprocating?
By Josip in forum Industrial CompressorsReplies: 18Last Post: 27-01-2009, 10:36 PM -
advantage of twin screw compressor over single screw compressor
By azzah in forum New to REReplies: 7Last Post: 23-09-2008, 09:24 AM -
Mono or twin screw
By Nirmalya in forum Industrial CompressorsReplies: 43Last Post: 12-09-2006, 03:19 AM