Results 1 to 4 of 4
  1. #1
    mikseidis's Avatar
    mikseidis Guest

    screw compressor CSH 75



    Hello
    I have a little problem with this compressor.
    the controler shows high discharge temperature.
    What can be possible failures



  2. #2
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: screw compressor CSH 75

    What are the operating conditions? what is the refrigerant?

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: screw compressor CSH 75

    Hi Mikseidis.
    There could be many reasons for your High pressure Fault.
    If the tranducer is reading correctly.
    The speed at which you observe the HP rise from start-up would be a good indicator.
    Also is this a stand alone system or 1 of several. etc.

    In no particular order
    lack of HP cooling, Cond. water / air?
    overcharged? (unlikely unless you have adjusted the charge).
    Air in the system?
    chocked liquid strainer?
    Condenser scaled or dirty?
    Moisture in the system?
    Faulty Expansion Valve (closed)?
    For example!
    Cheers Grizzly.

    For a better answer give us more info!

  4. #4
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: screw compressor CSH 75

    What AC/Refrigeration system you are using?,also the refrigerant?..,more info pls..
    <"No one is so smart, they just stay with problems longer and use their imagination">

Similar Threads

  1. VSD on screw machines
    By Mike Hopkins in forum New Technologies
    Replies: 14
    Last Post: 20-02-2011, 12:10 AM
  2. R22 - R417 (RetroFit) Screw set A.C
    By Chris_Atlantic in forum Trouble Shooting
    Replies: 3
    Last Post: 23-04-2010, 06:53 PM
  3. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 10:36 PM
  4. Replies: 7
    Last Post: 23-09-2008, 09:24 AM
  5. Mono or twin screw
    By Nirmalya in forum Industrial Compressors
    Replies: 43
    Last Post: 12-09-2006, 03:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •