    York YCL504155A5OYA Chiller RF leak?



    I was leak testing yesterday when I noticed the pipework between the drier and the TEV on circuit 1 on this chiller was cold 11deg c. (It was shut down). Looking in the sight glass you can see the refrigerant flashing off.
    Static pressures were

    CCT 1 LP 3.14 bar HP 3.1
    CCT 2 LP 3.0 HP 6.9

    Now is this caused by the pressures equalising accross the TEV when the plant is shut down or is this circuit leaking after the TEV? I have been unable to find a leak so far.



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: York YCL504155A5OYA Chiller RF leak?

    Hi there,

    Is the sight glass after the drier?
    You should check the filter, it might be blocked.
    cheers
    Even Einstein Asked Questions

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Replies: 3
    Last Post: 22-12-2008, 07:13 PM
  4. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Replies: 7
    Last Post: 13-12-2008, 03:43 PM
  5. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •