    Thumbs down HP/LP settings on R134a



    hey guys, finishing off an install of three new condensing units to three remote chillers, all identical on R134a. whats should i set the HP/LP switches to??



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: HP/LP settings on R134a

    What do the manufacturers of the chillers specify for the settings?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2009
    Location
    new zealand
    Age
    57
    Posts
    44
    Rep Power
    0

    Re: HP/LP settings on R134a

    If there is no manufacturers specs, then depending on whether the switches provide a control or safety function they will need to be set up to accomodate the operational requirements of the chillers ( You will need the operational specs of the chiller for this specific application)

  4. #4
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: HP/LP settings on R134a

    I agree with Dirk. You can refer the compressor operating envelope and set LP/HP according to the lowest and highest possible operating Presures.

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: HP/LP settings on R134a

    First you estimate the operating conditions i.e. evaporating temp and condensing temp.
    Set LP below the operating pressure and HP above the operating HP.
    If you set these very close to the operating conditions then you will get unwanted cut outs. Set them reasonably.
    Cheers
    Even Einstein Asked Questions

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: HP/LP settings on R134a

    High set can be 200psi.

    Low set depends on how the system stop and if there is an SV that runs parallel to the compressor or as a pump down control.

    Is it manual reset or automatic one?

    Bring more details and get better answers.

Similar Threads

  1. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 12:44 AM
  2. Clogged condenser leading to no gas on R134a systems?
    By runningonavac in forum Refrigerants
    Replies: 12
    Last Post: 01-09-2009, 10:52 PM
  3. r12 vs r134a minifridges (efficiency)
    By ziddey in forum Fundamentals
    Replies: 10
    Last Post: 25-06-2009, 06:26 AM
  4. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Replies: 0
    Last Post: 28-02-2005, 09:05 AM
  5. Replies: 5
    Last Post: 01-03-2004, 09:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •