Results 1 to 12 of 12
    dossak0a's Avatar
    dossak0a Guest
    Carrier 19XR CHILLER
    Hi, I have this problem on 600 ton chillers which are losing oil or should I say where it goes. We are adding refrigerant oil 2 gallons in a week. Pls. help or give ideas to troubleshoot. Thank you very much.
    Apr 2009
    israel
    778
    Re: Carrier 19XR CHILLER
    Hi :
    If u leave your condenser pump running when chiller is off oil might MIGRATE AND accumalate in evaportaor
    check your approach temp when unit is running u will probably find it very high in the evaporator
    good luck
    Jul 2010
    Boston
    I have a 19xrv chiller PIC-2 FRAME-3 with a wide evap. approach, dropped the cooler heads divider gasket was intact and okay pulled the charge, by weight its okay according to the name plate.Examined the float,and it was tight so I replaced the entire float Re-assemled made sure float pin and bubbler line lined up correctly, checked bubbler line with nitrogen,and it was clean.recharged 610 lbs 134A same probleme. Pulled charge again,checked liquid line ball valve for wear there was problemes with earlier machines and a service bulletin ,it was okay. Sent a camera through the evap liquid spray header it appeared to be clean.
    Does anyone have any Ideas?
    Thank you!!!
    Jul 2010
    Boston
    CW and CHW isolation valve close when machine is in the unocc mode pd and flow rates were within design
    Oct 2009
    merida mexico
    54
    282
    doos:
    what is your email address I send you newsletter service
    Jul 2010
    Boston
    Quote Originally Posted by serviceman View Post
    doos:
    scheylerproperties@hotmail.com or alex.chiller@ef.com
    Thank you
    chiller15's Avatar
    chiller15 Guest
    Newbie here............
    I'm having very similar increased approach problems on 3 different machines (1)19xr 3 comp & 4 size hx and (2)xrv size3 comp & size five hx.
    Evap approach stays consistent around 4 deg. design on the XR is 1.8 deg and the XRV's around 6.deg
    *Flow is w/ in design
    *added refrigerant then recovered it back. Due to discharge temp
    *check divider gasket - good
    I feel the float assembly inspection next?
    Anyhow any feedback would be much obliged
    Robert
    chiller15's Avatar
    chiller15 Guest
    whoops typo thats .6 deg approach on the XRV's
    Jul 2010
    Boston
    [quote=chiller15;203843]Newbie here............
    Robert[/qu
    Jul 2010
    Boston
    [QUOTE=TurboChiller;203875]
    Quote Originally Posted by chiller15 View Post
    Robert[/qu
    Robert, here it is in a nut shell what I found is that the oil that was manufactured by others was not correct,it was a mix of mineral oil with poe this caused the wide approach,in the evaporator,and stopped the heat trasfer in the evaporator. These machines have enhanced tubes and the mineral gets in the grooves of the tubes,and retards the transfer of heat.What I would reccommend is taking both a oil sample and a refrigerant liquid sample from the evaporator (not vapor)and send it to a qualified testing lab(United Refrigeration). It could be a float but before I pulled the charge and disassemble the float I would check the refrigerant and oil that is a lot easier then pulling the float assembly. If you find that you have mineral oil in the refrigerant,I would be glad to give you my procedure on how to clean up the evaporator.
    Robert if you find you have this probleme would you please let me know.
    alex.chiller@ef.com
    chillertechnology@gmail.com
    THERMO-MAN's Avatar
    THERMO-MAN Guest
    Hi im a newbie on here & currently struggling to find out how to post a new thread.....sounds stupid i know!
    But im looking for a maintenance manual for the carrier container unit NT42-334-10. Can anyone help?
    Thanks.
    Nov 2005
    New Zealand
    550
    Quote Originally Posted by THERMO-MAN View Post
    Thanks.
    At top left hand side of page you will see forums click on it then scroll till you see the category you want, click on it and you will see thread starter
  1. Replies: 12
  2. Carrier Chiller Moisture Problem
    By damo567 in forum Commercial
    Last Post: 22-01-2011, 08:58 AM
  3. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Last Post: 17-06-2010, 06:55 AM
  4. Carrier Chiller Help
    By superswill in forum Trouble Shooting
    Last Post: 18-01-2007, 10:06 PM
  5. Carrier chiller oil migration
    By lowtech in forum Industrial
    Last Post: 30-04-2006, 04:11 PM