Replacing old Copeland compressor
Hello,
I am working on a freezer with an old CRM3-0400-PFV-270 compressor installed on the unit. Its a High-temp R22 compressor, and it has been working well on the freezer.
I am more of an AC guy myself, now what do you chaps figure I should do? Should I replace it with a Copeland equivalent? Or buy a suitable Low-temp replacement compressor?
Granted the new Low temp compressor are all going to be r404A, which would mean I am going to have to flush the system of any remaining mineral oil
-
18-05-2010, 07:56 AM #2
Re: Replacing old Copeland compressor
The CR compressor is also a medium temp R502 which Copeland quit publishing information about years ago. It pumps 16,700 btuh at a -10 SST. Basically most high temp R22 compressors are also medium temp R502 with the exception of the scrolls.
If this unit worked okay then replace it with the new model CR53KQ-PFV and use R502/R408A.
If you want to use a genuine low temp model it is a CF12K6E-PFV which can use R404A/R502/R408.
I sold a many CR high R22 temp units using R502 for freezer applications back in the 80's. It just meant using a larger HP model than the true low temp models. I bet the condensing unit model you have is a 2 fan F3AD-0401-CFV.Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com
-
18-05-2010, 10:42 PM #3
Re: Replacing old Copeland compressor
can the old one not be repaired,or is there not someone who does service/exchange compressors.
-
19-05-2010, 02:42 AM #4
Re: Replacing old Copeland compressor
You say that it has been working well,if so why change it .
I have not checked the specs but if it is a high temp R22 compressor and you are using it on a low temp application and have no additional sucton cooling you will be running excessive discharge tempreatures this breaks down the oil eventually causing compressor failure. Iwould reccomend you convert to another suitable refrigerant ie 404a and suitable compressor.
-
19-05-2010, 02:46 AM #5
Re: Replacing old Copeland compressor
Sorry may have ****ed up was assuing unit is running on r22.
-
21-05-2010, 04:40 AM #6
Re: Replacing old Copeland compressor
As powell suggests, replace it with the correct CF low temperature model as we should all try to stick with more energy efficient solutions.. The Cr range is not designed for low temp applications and will run inefficiently.
Similar Threads
-
UK - Fridge/freezer, fridge warm - needs replacing??
By ken300 in forum DomesticReplies: 5Last Post: 04-11-2009, 07:21 AM -
Replacing R12
By mjpaolo in forum Technical SpeculationsReplies: 14Last Post: 09-06-2009, 06:58 AM -
replacing R12 comp with POE compressor
By Richvacr in forum CommercialReplies: 5Last Post: 02-05-2009, 07:04 AM -
Replacing a pari of compressors ona Carrier 30HR 121
By Sanshinman in forum CommercialReplies: 3Last Post: 06-11-2008, 06:50 PM -
Do we have some expert in replacing compressors
By Zahid in forum Air ConditioningReplies: 2Last Post: 01-07-2008, 07:59 AM