    Lennox RTU ???? What have I gotten myself into!



    Ok so I decided, you know what F it im gonna try and tackle this beast myself and see if I can fix it. Its a Lennox LGA120H2 10ton

    First problem: Leaking valve core on the discharge side
    2nd problem: 1 bad condenser fan

    Replaced leaking valve core,
    Evac'ed the system, then put a vacuum on the system. Charged (weight) in 11lbs 8oz.

    Compressor 1 -
    Discharge line: 84degree f; 375PSIG
    Suction Line: 180degree f; 70PSIG
    Evap Temp IN: 74degree f
    Evap Temp OUT: 83degree f
    Cond Temp IN: 185degree f
    Cond Temp OUT: 131degree f

    Can someone please tell me what is wrong? I believe the normal pressures at 75degree f ambient temp should be 76psig and 250psig.



  2. #2
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    Here is the Lennox manual:
    http://www.mediafire.com/?bjqrmywfzim

  3. #3
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    oops made an error:

    Discharge: 180degree f; 375PSIG
    Suction: 84degree f; 70PSIG

  4. #4
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    Outdoor temp aprox. 78degrees f

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Lennox RTU ???? What have I gotten myself into!

    Pressures mean nothing without knowing what refrigerant is in there.

  6. #6
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    r-22 hkjhkl

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Lennox RTU ???? What have I gotten myself into!

    Here is a list of the temps/pressures needed to troubleshoot a system:

    Evap air in temp
    Evap air out temp
    Low side pressure or saturation temp
    Suction line temp at evap outlet

    Cond air in temp
    Cond air out temp
    High side pressure or saturation temp
    Liquid line temp at receiver or condenser outlet

  8. #8
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    Sorry, I feel like an idiot, but could you please explain air in temps and air out temps? Are those the temps of the lines going in and out the condenser/evaporator? Sorry I am a visual learner and think way to deeply when it comes to something rather simple :/

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Lennox RTU ???? What have I gotten myself into!

    Quote Originally Posted by ZeroTolerance View Post
    Sorry, I feel like an idiot, but could you please explain air in temps and air out temps? Are those the temps of the lines going in and out the condenser/evaporator? Sorry I am a visual learner and think way to deeply when it comes to something rather simple :/
    It is exactly as it is written!

    Air in temp is temperature of air entering heat exchanger.
    Liquid line tem is temperature of line leaving condenser or receiver measured 10" from condenser/receiver.
    Etc..........

  10. #10
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    So evap and cond. air in temps will be the same? Which would be the outdoor ambient temperature?

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Lennox RTU ???? What have I gotten myself into!

    Quote Originally Posted by ZeroTolerance View Post
    So evap and cond. air in temps will be the same? Which would be the outdoor ambient temperature?

    What i do is hold the thermometer in front of the coil where the air is going in, thats your air in (or air on) to the coil, then hold the thermometer at the outlet of the coil, thats your air out (or air off) temperature.

    If you just assume that the ambient air temp is the same as the air in to the coils, there are times when due to siting of equipment, or the way the wind is blowing, or even fan motors running backward that your assumption causes a delay in finding the problem.
    Best measure it if at all possible.

    I learn better by seeing and doing too.

    Jon

  12. #12
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    Problem solved. Thanks guys! Again I am trying to get more knowledgeable in the trade and feel I have a pretty good grasp on the concepts of HVAC-R. Just need to fine tune my knowledge.

  13. #13
    Join Date
    Mar 2007
    Location
    USA
    Posts
    118
    Rep Power
    18

    Re: Lennox RTU ???? What have I gotten myself into!

    so what was the problem? In any forum we appreciate feedback.

  14. #14
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    Bad condenser fan LOL. SUPER SUPER STUPID mistake was on my manifold I unhooked the lines that go into the gauges and hooked them up to the unit BUT left the other side of the lines connected to the non functioning side of the manifold so I though I was evac'ing the system when I wasnt ROFL. GO ahead everyone laugh your ass off. To my defense I had only gotten 4hours a sleep the night before and was rushing trying to get to the next job.

  15. #15
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: Lennox RTU ???? What have I gotten myself into!

    Then I vacuumed the system then tried to weigh in the charge and more than likely overcharged the system

  16. #16
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Lennox RTU ???? What have I gotten myself into!

    hey buddy we have ALL been there before.. its a learning experience.. and this trade has a lot of things to learn.. but I wholeheartedly believe in learning as you do....

    if you have any budget at all I would say to go out and look into the field-piece line of HVAC tools.. they have some great tools that will help you with superheat,sub cooling, etc...

    be careful to always unhook the gauges from the unit first(before the manifold gauges) unless your hoses have check valves in them or you could get a refrigerant release or introduce air into an evac'd and vacuumed system....

    as you will learn and read from posts air and moisture in a refrigeration circuit are NOT a good thing...

    down in dallas you are dealing with huge amounts of humidity too... you will want to run the vacuum pump for a good long time if you are changing parts in the refrigeration circuits...
    -Christopher

Similar Threads

  1. Lennox wa230
    By james10 in forum New to RE
    Replies: 2
    Last Post: 12-06-2010, 04:46 PM
  2. Lennox BLV-17D
    By Birds in forum Air Conditioning
    Replies: 0
    Last Post: 15-02-2010, 04:42 PM
  3. Lennox Kp02 controller
    By fixit in forum Heat Pumps
    Replies: 1
    Last Post: 30-11-2009, 09:43 PM
  4. Lennox unit problem
    By marc5180 in forum Air Conditioning
    Replies: 35
    Last Post: 08-11-2008, 10:16 PM
  5. lennox fault code
    By richelli in forum Trouble Shooting
    Replies: 0
    Last Post: 01-02-2008, 09:13 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •