    Carlyle Compresser question



    Working on a Carrier 48TJ016-028 WITH A Carlyle Compresser. I have high discharge temp about 50 psi discharge pressure. No suction pressure or temp. The valves were leaking where the cover are to be hand tight. So basically high discharge temp low discharge psi no suction temp or psig. Any suggustions on what might be going on with unit .



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Carlyle Compresser question

    Hi there,

    From the symptoms you mentioned, probably there is not enough refrigerant in the system.
    The other case is that your evaporator is starved.
    Check the TEV, filter and refrigerant amount.

    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Carlyle Compresser question

    Low mass flow through compressor .

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carlyle Compresser question

    Quote Originally Posted by bwd111 View Post
    Working on a Carrier 48TJ016-028 WITH A Carlyle Compresser. I have high discharge temp about 50 psi discharge pressure. No suction pressure or temp. The valves were leaking where the cover are to be hand tight. So basically high discharge temp low discharge psi no suction temp or psig. Any suggustions on what might be going on with unit .
    Hi what model unit are we dealing with here?
    do you have exv or txv?
    it does sound like a lack of refrigerant ,
    is this a chiller or dx ?
    more detailes would be helpful
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    Just a roof top unit with a cap tube. Carrier with two compressors side by side. Tried to add refer but system has no suction pressure but hot discharge temp and 50 psig pressure. Suction line is not cold or warm. Same temp as outdoor temp. Could be

  6. #6
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: Carlyle Compresser question

    Quote Originally Posted by bwd111 View Post
    Just a roof top unit with a cap tube. Carrier with two compressors side by side. Tried to add refer but system has no suction pressure but hot discharge temp and 50 psig pressure. Suction line is not cold or warm. Same temp as outdoor temp. Could be
    There's no such thing as no suction pressure. Is it 5psig, 0psig, 10"hg? If the suction pressure is 0 psig, then it's at atomospheric pressure, which depending upon the units used is 1 atm, 14.7 psia, etc., etc. That isn't the same as no pressure. In that case it could be that there's a massive leak on the low side causing any added refrigerant to immediately blow back out into the atmosphere.

  7. #7
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    The compressor is not sucking so there is no suction comming from the unit . foo

  8. #8
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: Carlyle Compresser question

    Quote Originally Posted by bwd111 View Post
    The compressor is not sucking so there is no suction comming from the unit . foo
    "Suction pressure" is a poor choice of terminology, but then I didn't come up with it either. How about we call it the "low side pressure" instead. What was the low side pressure reading? Assuming that there is a low side, then it does not have "no pressure."

  9. #9
    beh25's Avatar
    beh25 Guest

    Re: Carlyle Compresser question

    if your discharge pressure is 50 psi and your suction is zero. the problem is refrigerant in the system is not enough,maybe your system have leak, or your txv, filter is clogging.

  10. #10
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    The low side pressure is the pressure of refer that is in the line. When energized the low side same as when the comp is off. The high side pressure is about 60 psi. I tried to put the comp in pump down mode but wouldn't. Usuallly if bad valve are culprit then unit would equalize very rapidly.

  11. #11
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    This is my diagnose: a DISCHARGE valve that isn't seating properly because of damage and is causing the low head pressure. Refer vapor is be forced out of the cylinder and into the discharge line during the up stroke of the comp. Then on down stroke of comp the same refer is drawn back in, That is why i have such a hot discharge line...

  12. #12
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Carlyle Compresser question

    but still 60 PSI on the high side and 0 PSI on the low side would indicate the system hasnt got enough gas to stand a chance.... ....

    if your suction pressure is staying at the same pressure as tyhe discharge line I would think along the lines of a discharge valve.......

    what do your low side and high side guages read when the unit is running?
    -Christopher

  13. #13
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carlyle Compresser question

    Hi bwd111 :
    did u try to manually pump down the unit by closing the valve?
    this will let you know if your plate is smashed,if you manage to pump down then u are short of refrigerant and i would look for a leek.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  14. #14
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    When high side is measured while running 50 psi and low side is the same off as is on. I tried to add gas and will not accept any. The vavle is backseated. Im thinking discharge valve is not properly seated.Refer vapor is be forced out of the cylinder and into the discharge line during the up stroke of the comp. Then on down stroke of comp the same refer is drawn back in, That is why i have such a hot discharge line...

  15. #15
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    I tried to pump down but wouldn't. I closed high side and wacthed the lowside and no drop in pressure. Usually you cant pump down unit and if fast equlizeation happens you would have bad valves. Any suggestions

  16. #16
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    High side while running is 50 and lowside has the same as while running and stop . The only pressure im ready is the temp/pressure of refer in the line. beleive it was 60 on lowside. Again refer temp/pressure relationship on a 85 degree day. I think its the discharge valve as well.

  17. #17
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Carlyle Compresser question

    Hi,

    I read that some people mentioned about the compressor valves...
    If it was the valve (either suction or discharge), suction pressure would go up and discharge pressure would go down. This is not happening here.
    Check the refrigerant first.
    Cheers
    Even Einstein Asked Questions

  18. #18
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carlyle Compresser question

    Quote Originally Posted by bwd111 View Post
    I tried to pump down but wouldn't. I closed high side and wacthed the lowside and no drop in pressure. Usually you cant pump down unit and if fast equlizeation happens you would have bad valves. Any suggestions
    Hi :
    the only advice based on your description would be to change a compressor !
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  19. #19
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Carlyle Compresser question

    Why don't you measure the subcooling, the system is obviously short of refrigerant, weigh out the charge for further confirmation.

    What about the LP switch, is there one? Has it been linked out?

    Cheers
    Tutto il Mondo e un Paese

  20. #20
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    It was low on refrigerant, trying to add refrigerant but cant add any if comp has no suction pressure. H ooked refer to lowside turned comp on and lowside pressure didnt go up or down. discharge line hot lowside was same temp as ambient.

  21. #21
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    If low pressure switch was not working the comp would not come on. Plus lps doesnt stop suction pressure and allow dischagre to discharge..

  22. #22
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Carlyle Compresser question

    What you are reporting is not adding up, make sure that the information you are providing is correct. you seem to not know what the low side pressure is, you have been asked repeatedly to tell us what it is and you have yet to give us a gauge reading. Also, if the refrigerant in the tank is at a higher pressure then the refigerant in the system you will add charge to the system. If you in fact cannot add refrigerant then you need to check your gauges because you have much more then 50- 60 psig in your system. Every indicator if I am deciphering them correctly leads one to believe that you must be low on charge.

  23. #23
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Carlyle Compresser question

    Hi,

    What do you mean you can not add refrigerant?

    Check the solenoid valve or hand valve on the liquid line, are they fully opened?
    Even Einstein Asked Questions

  24. #24
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Carlyle Compresser question

    Hi bwd111
    Is it possible that you have the suction service valve in the back seated position instead of cracked off the back seat to take a gauge reading? http://www.scribd.com/doc/13484919/C...Service-Manual will give you the ebook service manual which will be very helpful to you.

  25. #25
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carlyle Compresser question

    Quote Originally Posted by bwd111 View Post
    It was low on refrigerant, trying to add refrigerant but cant add any if comp has no suction pressure. H ooked refer to lowside turned comp on and lowside pressure didnt go up or down. discharge line hot lowside was same temp as ambient.
    Hi :
    looking through all the advice you got here you should check your main suction valve and gagues !!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  26. #26
    Join Date
    Aug 2009
    Location
    utah
    Posts
    83
    Rep Power
    15

    Re: Carlyle Compresser question

    Well how about this as NO one has yet to say. Acutrol refrigerant Metering Device that are located inside each one of the feeder tubes into the evap coils are fixed orfices and had a clog which caused blockage and that is why suction pressure was not moving on the guage. Only prussure i had was the temp/pressure relationship of the outdoor temp i was not looking for . I was looking for suction pressure from a good running comp.

  27. #27
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Carlyle Compresser question

    Quote Originally Posted by lana View Post
    Hi there,

    From the symptoms you mentioned, probably there is not enough refrigerant in the system.
    The other case is that your evaporator is starved.
    Check the TEV, filter and refrigerant amount.

    Cheers
    I told you to check that at the first post.
    Even Einstein Asked Questions

  28. #28
    tej310782's Avatar
    tej310782 Guest

    Re: Carlyle Compresser question

    i have carrier 5h-40 compressor it getting tripped on low oil pressure i top up oil then alsosame problem arise

  29. #29
    tej310782's Avatar
    tej310782 Guest

    Re: Carlyle Compresser question

    in my 5h-40 compressor ther is a formation of ice on suction side hp-215, lp-52, op-110 and i adjusted tev kept outside for superheating then also liquid line is not hot and ice form on evaporator coil what is the reason

Similar Threads

  1. Replies: 1
    Last Post: 02-06-2009, 04:01 PM
  2. Ice forming on compresser?
    By jbomba in forum Trouble Shooting
    Replies: 12
    Last Post: 27-04-2009, 01:25 AM
  3. Compresser electricals - HELP me please!!!
    By pjalchemist in forum Electrical
    Replies: 38
    Last Post: 28-11-2008, 12:09 PM
  4. Refriferation cycle question
    By ozmecheng in forum Fundamentals
    Replies: 32
    Last Post: 26-03-2008, 10:38 PM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •