    York ycam problem



    Hi there,

    I recently changed a compressor in a heat pump York Ycam 360.
    The compressor is a Copeland D8SJ-6000 with R22.
    After start up,i notised white foam in oil glass and the needle of the high pressure gauge instable.
    Also the muffler is in strong vibration.
    What could be the problem??



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York ycam problem

    Hi your instable needle could point that u have air in the sys,the foam could be liquid flood back
    and a vibrating muffler dosent sound good ,
    for a start i would revaccume the unit to low microns at least 500, make sure there are no leaks and then recharge .
    then check your pressures and make sure you are not over charged and make sure u dont have liquid flood back,
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: York ycam problem

    Thanks goshen.I charged the system by weight 41 kilos.
    System superheat is 10 celsious.The previous compressor had broken suction valves and damaged pistons.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York ycam problem

    Quote Originally Posted by goshen View Post
    Hi your instable needle could point that u have air in the sys,the foam could be liquid flood back
    and a vibrating muffler dosent sound good ,
    for a start i would revaccume the unit to low microns at least 500, make sure there are no leaks and then recharge .
    then check your pressures and make sure you are not over charged and make sure u dont have liquid flood back,
    good luck
    Hi in due of previouse damage u defenatly have liquid slugging ! check your liquid solonoied valve and txv setting .
    good luck if u catch it on time u will probably save yorself a compressor changing.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    teslareefer's Avatar
    teslareefer Guest

    Re: York ycam problem

    Dear All,,,,I have a problem with York YCAM 240 ..."external Interlock " .....can you help me with it ? ......Thanks

Similar Threads

  1. Replies: 20
    Last Post: 15-08-2010, 11:49 AM
  2. YORK ducted split
    By ALONEI in forum Trouble Shooting
    Replies: 7
    Last Post: 10-07-2010, 02:18 AM
  3. Help to solve problem on York chiller
    By nassersh in forum Trouble Shooting
    Replies: 7
    Last Post: 03-06-2008, 08:38 PM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •