Daikin Split inverter external unit fault
Hi anyone assist with the following?
The external unit is a RXD71JVEA , I have lifted the lid and found a few dead gecko's !!.
Closer inspection indicates that there are NO led's lit, and a component called DB1 it has ~~ and +- label on PCB. (assume this a rectifier)looks as though it has cooked.
Any idea's as to equivalents or what else I should look for that may be at fault.
The overall symptoms of the unit when switched on is that the green light flashes on the internal unit and nothing else. Error code is U4
Thanks
-
17-05-2010, 10:38 PM #2
Re: Daikin Split inverter external unit fault
it looks like the gekko has shorted out the main control printed circuit board, you will find that on that board there will be a fuse close to the power in that may be blown or one of the components on the board has shorted when shorted out by the gekko.
Looks like it si goind to be boards that you will need for that one.
-
18-05-2010, 10:47 AM #3
Re: Daikin Split inverter external unit fault
As suggested check control fuse 3.15amp on filter PCB. If this is ok then unplug the outdoor fan motor and try again, you may find that the green led starts flashing again if so outdoor fan motor is causing the problems.
Similar Threads
-
split inverter unsure of proper charge spec.. how to charge?
By cadillackid in forum Air ConditioningReplies: 4Last Post: 19-11-2009, 01:52 PM -
Daikin Fault on Commissioning
By mchild in forum Air ConditioningReplies: 16Last Post: 28-03-2009, 02:56 PM -
Split unit sensor explanation fault diagnosis?
By karl957 in forum Air ConditioningReplies: 8Last Post: 04-01-2009, 05:28 AM -
Daikin Cassette Fault
By symon22 in forum Air ConditioningReplies: 5Last Post: 23-05-2008, 06:19 PM