    walk in freezer compressor



    I have a walkin freezer and when the compressor goes into defrost, it doesn't turn back on automatically when defrost cycle in finished.
    we are having to push a button to restart it. This ssems to only happen when it is warm outside, being in phoenix this is approx 6 months a year, and had no problem during the winter



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: walk in freezer compressor

    Which button do you have to press to restart it? Describe the unit.

  3. #3
    phxjersey's Avatar
    phxjersey Guest

    Re: walk in freezer compressor

    it is a Russell 4 ton compressor,,up top near the fan, there is a small rectangle box with a button to restart, after the defrost cylce has ended, approx 30 min,, or so,,,we find out that after about 1 hour compressor hasnt restarted or kicked back, then we are having to climb on ladder and push button, then the fan and compressor goes back on,,,

  4. #4
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: walk in freezer compressor

    your condenser will be needing cleaned

  5. #5
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: walk in freezer compressor

    I'm not familiar with a reset button but rather a faulty contactor. Sounds like your pulling to many amps which is tripping the reset when the compressor tries to kick back on.

  6. #6
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: walk in freezer compressor

    Check your pressures in the system. Maybe high head pressure do to the outside heat?

  7. #7
    Join Date
    Sep 2007
    Location
    United States
    Posts
    167
    Rep Power
    17

    Re: walk in freezer compressor

    Check your defrost timer for cycle time and try to be there the next time it goes into defrost. Then test what circuit is open or tripped and follow back to find the cause. Have gauges on system to see if high pressure ramps enough to trip safety. Also connect clamp-on amp probe to check start-up demand. Finally...don't do any service before you test it. Use it as a learning experience. If you fix what you don't know is the problem, you will never know what happened. That way you have a jump on the next call. Good luck.
    Don't leave it like you found it.....Leave it like it should be !!!

  8. #8
    Join Date
    Aug 2009
    Location
    new zealand
    Age
    57
    Posts
    44
    Rep Power
    0

    Re: walk in freezer compressor

    As a rule you should know what fault you are rectifying before you press any reset device.

Similar Threads

  1. Testing Inverters
    By fridge doctor in forum Air Conditioning
    Replies: 38
    Last Post: 15-06-2011, 06:52 AM
  2. [Autocascade] Only a project ATM
    By before in forum CPU Overclockers
    Replies: 1
    Last Post: 07-05-2009, 11:13 AM
  3. compressor / electrical problem
    By Northdude in forum Commercial
    Replies: 6
    Last Post: 17-01-2009, 10:24 AM
  4. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM
  5. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •