    Carrier 19xr problem



    Hi all,

    I have a problem with Carrier Chiller 19xr5052cq3771. Chiller was stopped 6 months, when i switch power on comes alarm (Potential freez-up, evap press/temp too low). What i must to do?



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: Carrier 19xr problem

    chech gas charge/ check if the refrigerant has migrated to the condensor. open all valves and operate heaters check the calibration of the transducers (you can calibrate them using the pic 2 controller)

  3. #3
    -AL-'s Avatar
    -AL- Guest

    Re: Carrier 19xr problem

    I checked condenser (started sw pump, no ***** level presented). How i can check ***** level in evaporator? Al transducers calibrated. Main display shows evaporator temp. -24,5 c and condenser temp. -24,9 c. How is that possible?

  4. #4
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Carrier 19xr problem

    check water flow!

  5. #5
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: Carrier 19xr problem

    To check refrigerant level in the evaporator.
    1.Pull the Gas
    2.Attach a gauge line to the bottom of the evaporator and one at the top with an inline sight glass inbetween purge the air from the lines then raise and lower the sight glass this will indicate the liquid refrigerant level in the system.
    giving by your temperatures are your refering to water or refrigerant temps
    at -25 degreees C R134a is at 20kpa(0.3PSIG). If the transducers are correct sounds like theres no gas in the system

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Carrier 19xr problem

    Quote Originally Posted by -AL- View Post
    Hi all,

    I have a problem with Carrier Chiller 19xr5052cq3771. Chiller was stopped 6 months, when i switch power on comes alarm (Potential freez-up, evap press/temp too low). What i must to do?
    Hi i hope u didint blow your eprom memory ,this is a typical carrier problem if the unit sits with no powe for a few months this could happen and all u could do is call carrier ,in your case i hope you still have the memory so you should simply check all connections on controller side and then water side including pressure drop,and water filter if instaled .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  7. #7
    -AL-'s Avatar
    -AL- Guest

    Re: Carrier 19xr problem

    Hallo all,

    adding HEAT_EX display information:

    Chill water delta P 51,0 kPa
    Entering chill.w. 11,8 C
    Leaving chill.w 11,9 C
    Chill.w delta T -0,2 C
    Choll.w puppdown -0,1 C
    Evap.refr. t -26 C
    Evap. pressure 0,8 kPa
    Evap. approach 38,3 C
    Condens. w delta P 39,8 kPa
    Entering Condens. w 8,7 C
    Leaving Condens. w 8,5 C
    Condenser refrig. t -24,5 C
    Condenser pressure 8,3 kPa
    Condenser Approach -32,4 C
    Hot gas bypass ref. OFF
    Surge/HGP active? NO
    Active delta P 8,3 kPa
    Active delta T 0,3 C
    Surge/HGP delta T 0,3 C
    Head pressure reference 10%

  8. #8
    Join Date
    Jun 2006
    Location
    Australia
    Posts
    8
    Rep Power
    0

    Re: Carrier 19xr problem

    Looks like no gas to me.

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Carrier 19xr problem

    Quote Originally Posted by -AL- View Post
    Hallo all,

    adding HEAT_EX display information:

    Chill water delta P 51,0 kPa
    Entering chill.w. 11,8 C
    Leaving chill.w 11,9 C
    Chill.w delta T -0,2 C
    Choll.w puppdown -0,1 C
    Evap.refr. t -26 C
    Evap. pressure 0,8 kPa
    Evap. approach 38,3 C
    Condens. w delta P 39,8 kPa
    Entering Condens. w 8,7 C
    Leaving Condens. w 8,5 C
    Condenser refrig. t -24,5 C
    Condenser pressure 8,3 kPa
    Condenser Approach -32,4 C
    Hot gas bypass ref. OFF
    Surge/HGP active? NO
    Active delta P 8,3 kPa
    Active delta T 0,3 C
    Surge/HGP delta T 0,3 C
    Head pressure reference 10%
    Hi it would seem like a shortage of rerigerant!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  10. #10
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: Carrier 19xr problem

    Quote Originally Posted by james10 View Post
    chech gas charge/ check if the refrigerant has migrated to the condensor. open all valves and operate heaters check the calibration of the transducers (you can calibrate them using the pic 2 controller)
    HELLO

  11. #11
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Carrier 19xr problem

    valvual gauges placed on the refrigerant charge to check if you have coolant in the chiller

  12. #12
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: Carrier 19xr problem

    is there a frost stat needs re-setting ?

  13. #13
    -AL-'s Avatar
    -AL- Guest

    Re: Carrier 19xr problem

    Problem solved. Just adding gas!!!!

  14. #14
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: Carrier 19xr problem

    Quote Originally Posted by -AL- View Post
    Problem solved. Just adding gas!!!!
    Where was the leak? i presume you mean recharging and not simply adding gas to a leaking machine.
    If these machines are allowed to run with a low gas charge the compressor surges and if this happens you can kiss goodbye to your high speed shaft, guide vanes and impellor best part of £30k for the parts alone.

Similar Threads

  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  2. Samsung Vivace Problem AQV24VBCN
    By goldpau in forum Air Conditioning
    Replies: 0
    Last Post: 18-09-2009, 06:28 PM
  3. carrier ultima 53 problem
    By tito in forum Trouble Shooting
    Replies: 0
    Last Post: 08-08-2009, 04:07 PM
  4. Trane CCUH oil problem
    By wingman in forum Air Conditioning
    Replies: 25
    Last Post: 04-08-2009, 07:07 AM
  5. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •