    Hi all, My Fujitsu Ceiling Cassette AUT25RZAL keeps cycling off just when we need heat, if left on it eventually heats the room but is a damn nuisance. Shouldnt it keep heating untill it reaches cutoff temp of thermostat? thanks in anticipation
    Split Croatia
    57
    6,151
    36
    Re: Fujitsu Heating Problem
    What is outdoor temperature? Is it clean?
    If yes, put your gauges on it (when in cooling mode) and check pressure when on heating. Pay atention if pressure fall significantly when indoor unit fan start and rise again when cold air blowing prevention stops fan again. If yes, you are short of gas or you have restriction.
    Then recover gas and weigh it to establish if it is short of gas or restriction.
    Jun 2009
    Columbus Ohio
    55
    169
    15
    sounds exactly like Short charge to me.. those units will turn indoor fan on only if pipe temps are warm (88 degrees f i believe).. if the pipe temp drops below that the unit will kill the indoor fan till pipe temps warm up again...
    if it is short of gas you also might notice on cold days the outdoor coil freezes over very unevenly indicating early evaporation in the outdoor coil...
    -Christopher
    May 2010
    Russia
    168
    in cooling mode is OK?
    in heating mode outdoor fan is max-speed?
    in heating mode compressor is starting?
    Nov 2007
    Scotland
    43
    Is there no fault code showing in the controller?
    I'm going to a similar problem soon.
  1. Heating problem
    By exotiic in forum Air Conditioning
    Last Post: 21-08-2009, 07:44 AM
  2. Heating not working on split system what is the problem?
    By airflo in forum Air Conditioning
    Last Post: 22-07-2008, 06:42 PM
  3. r407c heating problem
    By marinetech in forum Trouble Shooting
    Last Post: 04-01-2008, 04:11 PM
  4. thermo acoustic refrigerator: problem with stack heating
    By jackal in forum Technical Discussions
    Last Post: 04-09-2006, 05:03 PM
  5. Heating problem
    By meadows in forum Trouble Shooting
    Last Post: 01-07-2006, 11:03 AM