    Problem with mc quay chiller.



    Hello guys.I have a problem with a mc quay water cooled chiller model ESH.D.120 and compressor model MQC 806 s.I started the system and after a minute it stopped from oil pressure.Suction pressure 4 bar,oil pressure 4 bar,disharge pressure 8 bar.Any idea why is this happening?Does anybody have the manual of that chiller or compressor??



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Problem with mc quay chiller.

    Just a few guesses

    Has the compressor been serviced lately? Is the oil pick up strainer clean?

    Is the oil sight glass level correct?

    Does the oil foam in the sight glass?

    Oil safeties are there for a purpose.

  3. #3
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: Problem with mc quay chiller.

    No oil pressure, should be about 6 to 8 bar above suction. If the compressor actually turned it could be that the oil pump is broken. There should be a linkage that sits in a slot on the end of the shaft to drive the oil pump.

  4. #4
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Problem with mc quay chiller.

    Thanks four your reply Frank.It is my first visit in this machine.I do not think that it has been serviced.The oil level is in the middle of the sight glass.No foam in the sight glass.Standing pressure of r22 is 7 bar.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Problem with mc quay chiller.

    Have you measured the oil pressure on start up?

    If you temporarily link out the oil control switch (2 minutes max above the knock out time) does the machine run?(to confirm that the switch is operational)

    What about operating pressures during start up - are they correct?

  6. #6
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Problem with mc quay chiller.

    The oil pressure on start up is the same with suction pressure.The operating pressures until the compressor stops are LP 4 BAR,HP 8 BAR.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Problem with mc quay chiller.

    Quote Originally Posted by HARRY 7 View Post
    The oil pressure on start up is the same with suction pressure.
    I would suspect then that the oil pump needs some attention.
    The oil pump should increase the oil pressure instantly on start up

  8. #8
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Problem with mc quay chiller.

    I agree with you Frank.But what about the refrigerant pressures?What do you believe about them?Thanks for your reply ptsac.

  9. #9
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: Problem with mc quay chiller.

    The pressures will be dependent on chilled water temp and ambient. Oil pressure should still be developing regardless of level of charge.
    Last edited by ptsac; 14-05-2010 at 08:41 PM.

  10. #10
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Problem with mc quay chiller.

    Temperature in water cooler 25 celcious.Temperature in cooling tower 30 celcious.

  11. #11
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: Problem with mc quay chiller.

    There maybe a problem with charge level, however there does appear to be an oil pressure problem that will require the compressor to be opened for inspection, this is the immediate issue.

  12. #12
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Problem with mc quay chiller.

    Thanks ptsac.Do you have the service manual of this compressor??

  13. #13
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: Problem with mc quay chiller.

    Unfortunately not, however look at Halltherms spares site
    http://www.mcquayinternationalparts....ucts/?cat=8130 you may get some idea from that.
    There is a sump pan filter for oil pump suction, Oil is then straight to the oil pump and then fed to a filter and pressure relief device before going to bearings etc. There could be a possibility that this assembly has not been tightened properly previously and oil is escaping from the assembly. This assembly is accessible from outside the compressor I think. Gas is still going to have to be removed as is oil. prepare for some mess.

  14. #14
    Join Date
    Dec 2008
    Location
    greece
    Age
    47
    Posts
    227
    Rep Power
    16

    Re: Problem with mc quay chiller.

    Thank you very much ptsac.
    I will check the site.But i still cannot understand the pressure difference.Don't you believe that high and low pressure are too close?
    Refrigerant 22 in the circuit

Similar Threads

  1. problem with multistack chiller
    By bright in forum Refrigerants
    Replies: 3
    Last Post: 30-10-2010, 10:43 PM
  2. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  3. Mc Quay ALS 213.2 Chiller
    By torrman in forum Air Conditioning
    Replies: 3
    Last Post: 15-02-2009, 08:13 PM
  4. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  5. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •