    Parallel oil system problem



    Feeling like a bit of a leech at the moment. The only times I have been here is for help. Promise this will change.

    Last year (June 09) I posted a problem with the oil system on a parallel rack in NY that we manufactured. The oil system blew the lines off at the levelers.

    This is a repeat of another rack in Lake Tahoe.
    This is a medium temp, 3 compressor equal scroll wc (5hp) rack. A cv valve was not installed, with a vent to the suction line (same setup as last time).

    The system has been in operation for 9 months without any major problems. Last night, an oil line at one of the levelers blew, dumping the oil, ref charge, etc. As the pressure in this line is equal to the suction pressure (very low), I'm thinking that the only possibility is hydraulic action. Oil flooding back so quickly that it blocks the vent line and blows at the weakest point (flare nut at the leveler).

    Has anyone seen something like this happen?

    When it happened last year, I thought it was a fluke. Evidently not. We have not used a P/R valve at the reservoir, nor have I seen them on other systems. I'm thinking that this may be a relatively inexpensive means to prevent this type of a catastrophic event from happening in the future.

    Anyone have a take on this?



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Parallel oil system problem

    Sounds like metal fatigue, with temp changes and vibration, flares are not good in that situation. Perhaps try retro fitting connects with flexibles.

  3. #3
    Join Date
    Jul 2009
    Location
    Portugal
    Age
    56
    Posts
    14
    Rep Power
    0

    Re: Parallel oil system problem

    Do you have liquid gas formation on the oil line, seen it happen because of liquid formation apoun standstill of compressores , reason no checkvalves on the main discarghe line,and if you donŽt have c7v valve maybe also the reason. use only flexible conections.

  4. #4
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Parallel oil system problem

    My company manufactures systems with oil return lines and we have used flexible lines for about 6 years with no brakages or blow outs. Before this we would suffer an occasional blow out due to fractures in the tube or on the flare itself. We now make up our own flexible lines for convenience. We also do the same for pressure control lines to the compressor.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. problem in Auto Refrigeration Cascade System
    By ernestlin in forum Trouble Shooting
    Replies: 17
    Last Post: 01-07-2009, 12:41 PM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. High Liquid Line Temperature
    By airefresco in forum Commercial
    Replies: 37
    Last Post: 11-02-2009, 04:36 PM
  5. Heating not working on split system what is the problem?
    By airflo in forum Air Conditioning
    Replies: 10
    Last Post: 22-07-2008, 06:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •