Results 1 to 4 of 4
Thread: McQuay Chiller help.
14-05-2010, 08:55 AM #1
Hi folks,
One of our guys needs some info regarding the capacity for a McQuay centrifugal chiller he is working on, any McQuay guys out there that can help us out would be much appreciated..thanks..
Model # PEH-087.E2417.2
Refrigerant R134A
LCHWT = 6DegC
RCHWT = 12DegC
ECWT = 22DegC
LCWT = 28DegC
14-05-2010, 07:59 PM #2
Re: McQuay Chiller help.
As far as I can see from the McQuay site it is 350-600 tons.
Product manual here..
http://www.mcquay.com/mcquaybiz/lite...pmpehpfh-1.pdf
they also have ops manual on the site.Brian - Newton Abbot, Devon, UK
Retired March 2015
14-05-2010, 08:56 PM #3
Ther are many vessel, and gear code options for the same model compressor so Shop order or style number would need to be referred to McQuay.
However do you know what the chilled water flow rate is in l/s.
6 x 4.19 x l/s = kw
17-05-2010, 03:04 PM #4
Thanks for the reply Brian i have sent him on the manual from your post so im just waiting on him to get back to me