    Motor running in reverse American Standard



    I have a 10 ton heat pump unit, about 18 months old. it has two condeser motors, one is running backwards. it is an American Standard machine. any ideas as how to rectify this problem.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Motor running in reverse American Standard

    hi aoneweb, are the motors single ph or 3ph?

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Motor running in reverse American Standard

    if it's three phase swap two of the phases over
    or is it configured to do this to prevent air being dragged through the second fan opening to direct the air through the condenser coil?

  4. #4
    Join Date
    Jan 2008
    Location
    England
    Posts
    25
    Rep Power
    0

    Re: Motor running in reverse American Standard

    Are both motors definitely running and pulling current?
    If one was not running the other blade can windmill effect in the air flow

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Motor running in reverse American Standard

    Duff capacitor on the one thats going backwards. When the caps go bad the motor has no starting torque so can either just sit there and hum, or start up in either direction especially if the wind gives it a little help.

    If the motors and capacitors are the same you could try swapping them to see if the problem follows the capacitor, make a note of where all the wire go before you start swapping things, or take a picture.

    Jon

  6. #6
    aoneweb's Avatar
    aoneweb Guest

    Re: Motor running in reverse American Standard

    Thanks for all your help, I will let you guys know of my progress.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Motor running in reverse American Standard

    Many American fan motors are running on two phase with 5mf capacitor.
    If you change the capacitor as Jon said, it should solve the problem.
    If the motor has two phase feed, you can not change direction.

  8. #8
    aoneweb's Avatar
    aoneweb Guest

    Re: Motor running in reverse American Standard

    I swapped the cables on the caps, now both motors are running in the same correct direction.
    I will monitor it.
    My supply temp started to drop right away, as it should.

  9. #9
    aoneweb's Avatar
    aoneweb Guest

    Re: Motor running in reverse American Standard

    Thank you all.

  10. #10
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Motor running in reverse American Standard

    now aint that a good feeling!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  11. #11
    Join Date
    Oct 2007
    Location
    mid-atlantic state, USA
    Posts
    6
    Rep Power
    0

    Re: Motor running in reverse American Standard

    Replace BOTH caps, and you will sleep better.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. subcooling and superheat are standard measurement or not?
    By karl2009 in forum Technical Discussions
    Replies: 3
    Last Post: 10-01-2009, 11:39 PM
  3. EN 378 revision
    By Argus in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 19-11-2008, 07:21 PM
  4. Very very strange??..an american perspective??
    By Superheatman in forum Chit Chat & Service Stories
    Replies: 18
    Last Post: 07-05-2006, 10:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •