    tx valves and liquid recievers



    do all tx valve systems NEED liquid recievers ? Even if a small charged system and no reason to ever have to pump down system... Is it absolutely vital ?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: tx valves and liquid recievers

    A lot of the Serap milk tanks i work on have txv's and no recievers, even on big 9 HP models.
    I have fitted a few txv's to cellar coolers when the capiliary has blocked up, just had to make sure the compressor had high starting torque electrics as txv don't equalise the pressure as quickly as capiliary when the system turns off.

    Why do you ask?
    Last edited by monkey spanners; 13-05-2010 at 01:27 PM.

  3. #3
    Join Date
    May 2010
    Location
    Queensland
    Posts
    36
    Rep Power
    0

    Re: tx valves and liquid recievers

    i just have a senior tradesman at work trying to tell me ALL tx valves NEED liquid recievers with no exceptions.... I have never heard such rule just need to hear other peoples thoughts.... thanks

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: tx valves and liquid recievers

    i dont think all tev systems need recievers but you have to make sure the sysem is corectly charged as the condenser will have to hold the liquid when the valve starts to close

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: tx valves and liquid recievers

    MArtinw58, I totally agree with you. Not needed if critically charged
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: tx valves and liquid recievers

    .

    You need to understand how the TEV works.

    It opens and closes so it needs more or less liquid.

    If it needs liquid then the liquid will need to come from somwhere, if it does not need liquid then the liquid will need to be stored somewhere.

    The liquid reciever is a good place but so is an oversized condenser..

    Coolrunnings.

    .

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: tx valves and liquid recievers

    Hi Young gun.
    despite what everyone else has said, senior tradesmen generally have figured problems out way back. Thats why they are still tradesmen.

  8. #8
    Join Date
    May 2010
    Location
    Queensland
    Posts
    36
    Rep Power
    0

    Re: tx valves and liquid recievers

    Hi Magoo,
    Yes i defintly listen to and take in everything i can from what other tradesman ( especially senior ) tradesman say. But I also like to study and ask other opinions, as just because they say and believe that, doesn't make it 100% correct, or relevant to all situations.
    Thanks Magoo

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: tx valves and liquid recievers

    Quote Originally Posted by young gun View Post
    Hi Magoo,
    Yes i defintly listen to and take in everything i can from what other tradesman ( especially senior ) tradesman say. But I also like to study and ask other opinions, as just because they say and believe that, doesn't make it 100% correct, or relevant to all situations.
    Thanks Magoo
    Well done, and how true!
    You should go far.

  10. #10
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: tx valves and liquid recievers

    Quote Originally Posted by cool runings View Post
    .

    The liquid reciever is a good place but so is an oversized condenser..
    You are right. If no reciever then part of condencer flooded (take part of reciever). Excess of thermal expansion of refrigerant are situated in condencer. In some systems after condencer (if no reciever) install pipe with bigger diameter.
    Last edited by Aik; 15-05-2010 at 07:53 AM.
    In some places will have to think ...

  11. #11
    Join Date
    May 2010
    Location
    Queensland
    Posts
    36
    Rep Power
    0

    Re: tx valves and liquid recievers

    Thankyou very much everyone for your thoughts.
    I totally understand how a TXV system could function without a reciever.
    So no one has ever been taught that ALL TXV systems MUST have a liquid reciever with no exceptions. Or no one has ever come across this in an old text book?

  12. #12
    Join Date
    May 2010
    Location
    Queensland
    Posts
    36
    Rep Power
    0

    Re: tx valves and liquid recievers

    Just found another thread on this subject.
    Receiver! Needed or not (Under Fundamentals)
    This also agree's with the fact not ALL txv systems need recievers.
    LOL Why am i having such a hard time trying to explain this at work.
    Maybe ill keep my thoughts to myself, and let them believe what they want to believe?

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: tx valves and liquid recievers

    Quote Originally Posted by young gun View Post
    LOL Why am i having such a hard time trying to explain this at work.
    Maybe ill keep my thoughts to myself, and let them believe what they want to believe?

    For some people, winning an argument or discussion is more important to them than being correct, which is a shame because they never progress and just stay with the level on knowledge they have.

    I love it when i find out i was wrong about something because thats when i stop being wrong and start being right

    Jon

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: tx valves and liquid recievers

    Young gun.
    OK ,you have a system that has a thermal expansion valve, aka TXvav. That txv is a constant modulating orifice, temp driven.
    Next, at high load the TXV is wide oen looking for max perfomance, as in pull down situation.If lacking liquid to feed the vav, the vav hunts. [ open to closed rapid cycling.]
    At design temp the TXV is at minimal open.
    So if you charge system for pull down, where the hell is that excess liquid going to stored. In the condenser obviously. So now effective condenser HX has been seriously reduced, creating a false high discharge condition.
    Problem: system can hydraulic. Conditions, ie overnight, winter, what ever. Now you have a vertual bomb at your disposal.
    Next people killed, you are on a mission to know were, kiss the family good by and go straight to jail.
    All for the sake of a friggen receiver.
    Really a no brainer decission.

  15. #15
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: tx valves and liquid recievers

    Arguments given here are very interesting and also true.

    WHAT IS CORRECT IS NOT ALWAYS POPULAR,
    WHAT IS POPULAR IS NOT ALWAYS CORRECT

    I have the same arguments with older engineers who know something (EITHER CORRECT OR INCORRECT) and they insist on it without any good reason.

    Anyway, having receiver in a TEV system is a good thing and also saves a lot of time and worries.
    In theory you may not need receiver BUT you have to charge the system critically, like cap tube system.
    If it is overcharged then excess refrigerant will accumulate in the condenser and you may have high pressure problem.
    Systems with water cooled condensers (shell & tube) usually don't have receivers because condenser also acts as receiver.

    In my opinion the difference (or advantage) between TEV system and cap tube is this very reason. Life is more easy with TEV than cap tube.

    Cheers
    Even Einstein Asked Questions

  16. #16
    Join Date
    Aug 2009
    Location
    new zealand
    Age
    57
    Posts
    44
    Rep Power
    0

    Re: tx valves and liquid recievers

    If you have constant load on the evaporator and relativly stable condensing it may not be neccessary to have a reciever. Under different load conditions there will be a varying amount of refrigerant in either the evaporator or condensor hence the need for the reciever.

  17. #17
    Join Date
    May 2010
    Location
    Queensland
    Posts
    36
    Rep Power
    0

    Re: tx valves and liquid recievers

    Toyota, Isuzu airconditioning and other car manufacturers also have gone away from the traditional drier reciever concept, and use the condenser as liquid reciever. Although not quite sure how the pipes have been modified at the end of the coil because i have not cut one up, either way its still a condenser coil being used partly as a liquid reciever.

    I think now it is quite obvious that ' you cannot generalize ALL tx valve systems as MUST NEED liquid recievers.'
    Because quite obviously all systems are different, they all face different heat loads and heat load changes and also face different condensing loads/situations.
    To generalize "ALL" tx valve systems with one rule, to me now sounds quite unprofessional and incorrect.

    But once again, that is just my opinion, which doesnt make it right.

  18. #18
    Join Date
    Dec 2009
    Location
    KUWAIT
    Posts
    10
    Rep Power
    0

    Re: tx valves and liquid recievers

    hi there,
    not atall.mostly large refrigeration system some time using depends on the tonnage of the system. but small tonnage it is not required.
    best rgds.
    bm

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Liquid charging through the suction side
    By deu58 in forum Fundamentals
    Replies: 13
    Last Post: 02-07-2010, 05:23 AM
  3. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •