Thread: Water in pipes!

  1. #1
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Water in pipes!



    An engineer removed a condenser for repairs and sealed off the 3x circuits on a Daikin Multi-system.

    Came back a week later to reinstall condenser with new parts and found that some plank had removed the taped up/plastic sheet covering over each of the circuit pipes. Open ends! Not just that: water in the first 6 inches of each pipe!
    He poured out an eggcup-full from each one.

    But the condenser was safe.

    The plan is to: a) blast the circuits with nitrogen to purge out as best he can any water or moisture in the pipe runs to the room units, b) connect up the condenser, with a drier on each circuit, c) pressure test and d) vac vac vac until there is no sign of moisture in the system (ie Tor gauge).

    That sound adequate?
    Last edited by Makeit go Right; 09-05-2010 at 12:21 PM.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Water in pipes!

    I would separately make vacuum drying on each circuit before connecting condensers and put driers only after vacuum drying to 300 microns (and holding to 700 microns isolated from vacuum pump for more than 24 hours) each one. Than make pressure test and final vacuum drying as nothing has happened. Then regularly check driers for temperature drop across them, because oil residue in open pipes has probably absorbed lot of moisture, and only way to dehydrate oil is by changing driers.
    Last edited by nike123; 08-05-2010 at 12:15 AM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Water in pipes!

    It has to be said that sealing pipes with plastic is not the way to go.

    I would be wary of 'blasting' the pipes as it might push something further into the system. Perhaps a slow bleed to clear the air and follow Nike's suggestion.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2008
    Location
    IRELAND
    Posts
    70
    Rep Power
    17

    Re: Water in pipes!

    Would there not be dirt in the pipes also? Possibly insects etc. Blasting is probably a good idea. Couldnt do any harm might also blow any water out. Maybe cut off a few meters of pipe and rebraze?

  5. #5
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Water in pipes!

    cutting off a few metres of pipe will not remove contamination of oil in the rest of the pipework.the oil needs to be removed and as far as i know the only way of doing this is by flushing.
    mmm to beer or not to beer...........lets drink breakfast

  6. #6
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Water in pipes!

    the oil must be changed, otherwise, you will have an acidity problem in the midterm.
    We have developed a special procedure/method to clean out water from AC plants.
    check this video:
    http://www.fri3oilsystem.com/ingles/video/video.html

  7. #7
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: Water in pipes!

    Yes, the engineer should have brazed off the pipe ends – he realises that now, of course.

    As for the remedy, a full cleanout/flush would be the best result, probably, but I cannot see this customer being willing to pay a large repair invoice (regardless of his accidental sabotage).

    I think we will trim back the tails as much as we can (maybe 10-12 inches could come off), which is where the water collected. And, being at the bottom of these circuits, the nearby oil would have been somewhat gravitating down to that low point too (a bit). But a trim can only assist things. Then some nitrogen (maybe slow maybe blasting) to help dry things out, at least, and then Nike’s plan, with triple-vac until we get a good result.

    Review things after running for a few days, ie check the driers in case they need a change, check oil acidity.

  8. #8
    Join Date
    Feb 2006
    Location
    Berkshire
    Posts
    37
    Rep Power
    0

    Re: Water in pipes!

    I might be wrong, but isnt the expansion device in the condensor and won't fitting the driers in the pipework outside the condensor effect cooling performance? Or will this be negligable?

  9. #9
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Water in pipes!

    there are no residue solvent cleaners on the market that are reasonably cheap and effective,two flushes the jobs done,no further drier changes,oil tests etc.you can walk away with complete confidence with the repair.
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. chart for PVC pipes closed chilled water system
    By mackistired in forum Air Conditioning
    Replies: 4
    Last Post: 14-11-2009, 03:23 AM
  3. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •