    How to charge sistem when you don't know right needed amount of refrigerant?



    Hi,

    Need advice how to charge system when you don't know right needed amount of refrigerant?
    Have old chiller for cooling water, need to change compressor and convert system from R22 to R407, but here is no information about amount of refrigerant.
    Have some liquid in suction line so I suspect overcharging or maybe TEV failure.
    Is obligatory change TEV when converting system from R22 to R407?



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    do have sight glass? if yes , you have to charge it untill is full, if not you have to use Evap. Temp. (suction press.) + Delta T = room temprature
    Make sure you TEV Is working and use a right one R 407 nor R 22.
    ((if you can hear soud of TEV , in short liquid TEV nose (sound) comes down and goes up))
    Last edited by mbc; 11-05-2010 at 06:36 PM.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Quote Originally Posted by mbc View Post
    do have sight glass? if yes , you have to charge it untill is full, if not you have to use Evap. Temp. (suction press.) + Delta T = room temprature
    A new one on me.....does it work?

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Hi there,

    There is a speculation that with Zeotropic blends (400 Series) the sight glass shouldn't be full otherwise the system is overcharged.

    For correct system charge you have to observe many things at the same time. Of course if all the components are selected correctly.

    1- Suction pressure according to design.
    2- Discharge pressure according to ambient temp or water temp. If there is a head pressure control then you have to stabilize condensing pressure for a while so you can measure sub-cooling.
    3- Super heat
    4- Sub-cooling
    5- Sight glass

    This job needs experience and knowledge at the same time. It is not very complicated.
    If you charge the system in winter then overcharging is a possibility but if you know what you are doing then it will be OK.

    Cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    The TEV of R22 may stay, but the charge is far less whit R407C then whit R22.
    The pressure for R407C is higher. it is difficult to charge on the sight glass, the system is to quicly overcharged.
    best way is to calculate the needed amount of cooling, and the possible amount of the unit. also keep in mind that you have some capacity loss on R407C.

    Ice

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    In addition to lana's correct answer above check compressor current (rated) and aim for an evap split (out - in) of 5.5k at 90% - 100% of load. Roughly 6k superheat at comp inlet and 10k subcooling. Depending on compressor. If you need more detail provide us with details of chiller and compressor.

  7. #7
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    if you have a reciever on the system check if it has a plate on it with volume in liters you can only fill to about 80% rull of thumb 1 lt = 1kg of refrigerant
    if there is on head pressure control head pressure needs to be about ambiant temp + 15 oC converted to pressure
    Last edited by martinw58; 12-05-2010 at 04:28 PM. Reason: extra infomation added

  8. #8
    Join Date
    Apr 2010
    Location
    Vilnius
    Age
    49
    Posts
    14
    Rep Power
    0

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    It's very simply system without reciever. TEV was broken, chenged it and charge system according sight glass. It took some time.
    After charging measured some data.
    LP 4,6 Bar
    HP 18,5 Bar
    Temp after condenser 41 C
    Temp after evaporator 14 C
    Temp in condenser 29,2 C
    Temp out condenser 41 C
    Water temp 21
    Data can be inaccurate due to "accuracy" of instruments.
    Compresor copeland ZR81

  9. #9
    Join Date
    Apr 2010
    Location
    Vilnius
    Age
    49
    Posts
    14
    Rep Power
    0

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Air Temp in condenser 29,2 C
    Air Temp out condenser 41 C

    Quote Originally Posted by nerijust View Post
    Temp in condenser 29,2 C
    Temp out condenser 41 C

  10. #10
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Check with the equipment manufacturer.
    Last edited by hvacrmedic; 19-06-2010 at 06:16 AM.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Quote Originally Posted by nerijust View Post
    It's very simply system without reciever. TEV was broken, chenged it and charge system according sight glass. It took some time.
    After charging measured some data.
    LP 4,6 Bar
    HP 18,5 Bar
    Temp after condenser 41 C
    Temp after evaporator 14 C
    Temp in condenser 29,2 C
    Temp out condenser 41 C
    Water temp 21
    Data can be inaccurate due to "accuracy" of instruments.
    Compresor copeland ZR81
    4,6 barg= 6,1°C (dew point)
    18,5 barg= 44,7°C (bub point)

    44,7-41 is 3,7 K Subcooling

    14-6,1 is 7,9 K Superheat

    Wait until water temperature is 2-3K near design temperature and check again subcooling and superheat.
    If that is your design temperature than subcooling is low and you need to add more refrigerant until subcooling became about 8K.
    Than check again superheat.
    Last edited by nike123; 15-05-2010 at 10:49 AM.

  12. #12
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    If that is your design temperature than subcooling is low and you need to add more refrigerant until subcooling became about 8K.

    Dear Sir,
    I am not clear at all; I learned from this forum that sub cool temp should be between 2-5 K.>>
    How u calculate all this?>>
    (4,6 barg= 6,1°C (dew point)
    18,5 barg= 44,7°C (bub point)

    44,7-41 is 3,7 K Sub cooling, 14-6,1 is 7,9 K Superheat)
    Plz. Explain and make simple for us.What is the best possible way to charge a undercharge system?

  13. #13
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    The acceptable degree of sub-cooling will depend on the condenser design. This is important.

    The balancing sub-cooling will also depend where in the operating cycle the system lies. Some condensers fill, others empty, during a moving rhvac cycle. It depends on the system.

    Using overly simplistic rules of thumb will, in all likelihood, lead to system over-charging.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Quote Originally Posted by Bashir01219 View Post

    Dear Sir,
    I am not clear at all; I learned from this forum that sub cool temp should be between 2-5 K.
    http://www.refrigeration-engineer.co...2&postcount=13

    http://www.refrigeration-engineer.co...ad.php?t=19701

    How u calculate all this?
    (4,6 barg= 6,1°C (dew point)
    18,5 barg= 44,7°C (bub point)
    http://www.centrogalileo.it/nuovaPA/...%20inglese.doc

    44,7-41 is 3,7 K Sub cooling, 14-6,1 is 7,9 K Superheat)
    Plz. Explain and make simple for us. What is the best possible way to charge a undercharge system?
    http://www.mediafire.com/?wzgtwmyhzty

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Quote Originally Posted by desA View Post

    The balancing sub-cooling will also depend where in the operating cycle the system lies. Some condensers fill, others empty, during a moving rhvac cycle. It depends on the system.


    Could you please elaborate on this little more.

  16. #16
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Originally Posted by desA
    The balancing sub-cooling will also depend where in the operating cycle the system lies. Some condensers fill, others empty, during a moving rhvac cycle. It depends on the system.
    Nike replied:
    Could you please elaborate on this little more.
    With pleasure.

    What happens in the condenser, and the amount of sub-cooling it will manage, will depend on the type of condenser, and the high-side (HP) system pressure drop.

    If the HP pressure drop is fairly low, then as pressure builds up in the condenser, it can be that the net liquid balance in the condenser reduces as HP rises. This can tend to lower the liquid level in the condenser, & so that amount of sub-cooling that the condenser will deliver.

    In a heat-pump, for instance, it will not be unusual to see a high SC at start of heating cycle, but a much lower value towards the end of the heating cycle. The amount of SC can reduce to the point of 0K, if the system has insufficient charge. Here, one must be careful to charge enough for the hot operating condition, but not so much as to raise the cold operating condition too much. Practically, the heat-pump will run mostly at hot condition, so this is the more important SC to watch.

    For a restrictive HP pipe system, the opposite effect can occur ie. the condenser backs up & SC rises over the cycle.
    Last edited by desA; 25-05-2010 at 09:57 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    @desA

    Thanks!

  18. #18
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    ^ It's a pleasure.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  19. #19
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Quote Originally Posted by Bashir01219 View Post
    How u calculate all this?
    (4,6 barg= 6,1°C (dew point)
    18,5 barg= 44,7°C (bub point)


    http://www2.dupont.com/Refrigerants/...mo_prop_si.pdf

  20. #20
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Thanks Sir,
    But i try but can't understand.......

  21. #21
    Join Date
    Sep 2007
    Location
    Brisbane, Australia
    Posts
    44
    Rep Power
    0

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Alot of water chillers are designed with plate heat exchangers which are too small - and means the unit is heavily reliant on the water pump providing a high enough flow rate of water to supply sufficient load to the evaporator.

    If the pump becomes inefficient for any reason (blockages, wear, restriction on inlet) you will find the metering device (typically TX valve) cannot maintain the correct superheat due to low / no load and can result in liquid flooding back to the compressor. This is why suction line accumulators are so incredibly important on water chillers (sized to hold the entire liquid charge!).

    If you are getting liquid flood back, and you have a plate heat exchanger, it may pay to check the flow rate of water through your evaporator.

    Otherwise its just a matter of applying basic refrigeration principles as outlined above.

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Quote Originally Posted by Bashir01219 View Post
    Thanks Sir,
    But i try but can't understand.......
    Dear Bashir, i think that you need some tutor to guide you thru your learning. It appears that you are thrown in field on which you are not up to requirement.
    I am strong supporter of your will to learn on what you actually doing, but you cannot expect to deal with that project only with advice given here. Advice is advice, not solution.

  23. #23
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: How to charge sistem when you don't know right needed amount of refrigerant?

    Quote Originally Posted by nike123 View Post
    Dear Bashir, i think that you need some tutor to guide you thru your learning. It appears that you are thrown in field on which you are not up to requirement.
    I am strong supporter of your will to learn on what you actually doing, but you cannot expect to deal with that project only with advice given here. Advice is advice, not solution.
    Thanks a lot Sir, In Bangladesh there is no training center on HVAC system. Most of the company doing their maintenance through third party, even sometime we too, but I didn’t like it, today or tomorrow I will learn whatever I want to learn, and for this purpose I need your help, I believe you can help me.
    basher.abdullah@radiant.com.bd

Similar Threads

  1. super heat and overcharge help for a noob
    By frostedflake in forum Trouble Shooting
    Replies: 11
    Last Post: 12-03-2009, 08:51 PM
  2. Rule of Thumb on Refrigerant Amount
    By rickmor in forum Refrigerants
    Replies: 7
    Last Post: 19-12-2005, 11:18 AM
  3. Calculating refrigerant charge
    By Consultant in forum Refrigerants
    Replies: 2
    Last Post: 10-05-2005, 03:39 PM
  4. refrigerant charge
    By pirestani in forum Refrigerants
    Replies: 1
    Last Post: 02-06-2002, 02:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •