    AAF HEPA filter
    anyone know what is the final pressure drop of the HEPA can be defined? I had a problem of setting the filter clogged alarm, are the setting related to your fan curve.
    Now my exhaust fan is operating with a frequency inverter at 40Hz which can achieve the exhaust flow rate with new HEPA filters, i.e. not in full load condition with a static pressure locate at mid stream of air duct to control the frequency inverter.
    I plot the fan curve had about 700pa differrential between the full load speed fan & 40Hz speed.
    As the AAF web site do not have the final resistance figure or graph of the ASTROCEL I filter,
    CAN ANYONE HELP? THANK YOU
    vB Code is ON
    Oct 2003
    5,630
    34
    Re: AAF HEPA filter
    Try perhaps at http://www.camfilfarr.com/script/main.as and let us know their answer. We all could learn of it.
    Jul 2001
    hong kong
    65
    27
    Smile Re: AAF HEPA filter
    thank you for your advice, i had calibrated the pressure drop alarm to 470pa, waited to see the next round of maintenance to review the pressure drop in next 3 months, we shall also check the negative pressure can be kept or not?
    vB Code is ON
  1. Attention! Air Conditioning Filter Experts I Need Help
    By hoffa4444 in forum Air Conditioning
    Last Post: 10-07-2006, 09:43 AM
  2. special air filter
    By 27143721 in forum Technical Speculations
    Last Post: 12-06-2006, 07:09 AM
  3. Ruptured oil filter
    By cooltrain in forum Trouble Shooting
    Last Post: 30-10-2003, 07:02 AM
  4. Stainless Steel Filter Body
    By Derek in forum Industrial
    Last Post: 10-04-2003, 06:25 PM
  5. DW Copeland
    By Abe in forum Trouble Shooting
    Last Post: 19-11-2002, 02:54 PM