    wusel's Avatar
    wusel Guest
    Question Staging TT300 at high pressure ratio
    Hi everybody and greetings from Germany,
    we have worked on process cooling units with Danfoss Turbocor TT300 for quite a while. As most of our applications are air-cooled condensers we are operating at high-pressure ratios in summer. We have problems bringing a second or third TT300 in whilst one is already running. Before I provide more details I want to ask if anyone has experience with this szenario and how to solve problems with "Front Radial Bearing Fault".
    Thanks for any comments in advance!
    Markus
    Jul 2004
    Netherlands/Germany
    8
    Re: Staging TT300 at high pressure ratio
    Hi markus,
    did you re-calibrated the bearings, and check the Amps off the bearings. frontbearing for TT300 pin 1-2 (2,75ohm - 3,00ohm) pin 3-4 (2,75 ohm - 3,00 ohm) if this not helps then check the BMCC and/or the PWM modul.
    coolMCX's Avatar
    coolMCX Guest
    Hi Marcus,
    Staging at high pressureratios is not allowed. You need to respect a maximum pressure ratio of 2.1 before starting additional compressors.
    Mar 2008
    34
    63
    I don't know how much this helps, but we use electronic gate valves on the discharge line, with a bypass line back to the compressor suction which allows the starting compressor to build up a pressure ratio before opening it to the discharge line, and the rest of the system.
  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Last Post: 19-07-2011, 03:16 AM
  2. Compression Ratio
    By Deano240 in forum Training
    Last Post: 18-11-2009, 05:09 AM
  3. Too high external static pressure
    By racknovice in forum Air Conditioning
    Last Post: 26-08-2007, 09:20 AM
  4. High head pressure no duty
    By LRAC in forum Commercial
    Last Post: 23-07-2007, 12:12 AM
  5. hvac/r terminology
    By Prof Sporlan in forum Fundamentals
    Last Post: 06-04-2002, 03:47 PM