    Question Staging TT300 at high pressure ratio



    Hi everybody and greetings from Germany,

    we have worked on process cooling units with Danfoss Turbocor TT300 for quite a while. As most of our applications are air-cooled condensers we are operating at high-pressure ratios in summer. We have problems bringing a second or third TT300 in whilst one is already running. Before I provide more details I want to ask if anyone has experience with this szenario and how to solve problems with "Front Radial Bearing Fault".

    Thanks for any comments in advance!

    Markus



  2. #2
    Join Date
    Jul 2004
    Location
    Netherlands/Germany
    Age
    61
    Posts
    8
    Rep Power
    0

    Re: Staging TT300 at high pressure ratio

    Hi markus,
    did you re-calibrated the bearings, and check the Amps off the bearings. frontbearing for TT300 pin 1-2 (2,75ohm - 3,00ohm) pin 3-4 (2,75 ohm - 3,00 ohm) if this not helps then check the BMCC and/or the PWM modul.

  3. #3
    coolMCX's Avatar
    coolMCX Guest

    Re: Staging TT300 at high pressure ratio

    Hi Marcus,
    Staging at high pressureratios is not allowed. You need to respect a maximum pressure ratio of 2.1 before starting additional compressors.

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Age
    34
    Posts
    63
    Rep Power
    17

    Re: Staging TT300 at high pressure ratio

    I don't know how much this helps, but we use electronic gate valves on the discharge line, with a bypass line back to the compressor suction which allows the starting compressor to build up a pressure ratio before opening it to the discharge line, and the rest of the system.

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Compression Ratio
    By Deano240 in forum Training
    Replies: 8
    Last Post: 18-11-2009, 05:09 AM
  3. Too high external static pressure
    By racknovice in forum Air Conditioning
    Replies: 8
    Last Post: 26-08-2007, 09:20 AM
  4. High head pressure no duty
    By LRAC in forum Commercial
    Replies: 15
    Last Post: 23-07-2007, 12:12 AM
  5. hvac/r terminology
    By Prof Sporlan in forum Fundamentals
    Replies: 18
    Last Post: 06-04-2002, 03:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •