    Low temp one off



    Hi, I've been asked to look at building a one off piece of lab equipment which require two walls about two foot high which atmospheric particles will pass through and freeze.
    One wall needs to be colder than the other, one at -60C and one at -40C the temperature needs to be very even from top to bottom.
    Also it needs to be cheap!
    I was thinking of flooded evaporators to give the even spread, the heat load is very low as the chamber will be well insulated with just a small amount of air being injected into it.
    What are your thoughts on getting -60C, can it be done with a single circuit (space is also an issue as it needs to be used on a plane).

    Thanks.



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Low temp one off

    Quote Originally Posted by Simon Butler View Post
    Hi, I've been asked to look at building a one off piece of lab equipment which require two walls about two foot high which atmospheric particles will pass through and freeze.
    One wall needs to be colder than the other, one at -60C and one at -40C the temperature needs to be very even from top to bottom.
    Also it needs to be cheap!
    I was thinking of flooded evaporators to give the even spread, the heat load is very low as the chamber will be well insulated with just a small amount of air being injected into it.
    What are your thoughts on getting -60C, can it be done with a single circuit (space is also an issue as it needs to be used on a plane).

    Thanks.
    I have done similar types of work, you combine 2 different types of refrigeration effect.
    -40C by vapour compression (normal say using R404a) for both plates, then you cascade thermoelectrics on to one of the plates to make your -60C (or colder if required) Bad timing I was in Manchester last week would have shown how, back in NZ now
    Last edited by mad fridgie; 10-05-2010 at 10:53 PM.

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  3. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Replies: 13
    Last Post: 10-05-2008, 04:22 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. cold room temp & the product temp
    By smpsmp45 in forum NH3
    Replies: 9
    Last Post: 21-09-2007, 11:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •