    404a Charging CONFUSION



    I've read so much different BS on how to charge a liquid (404a) into a system its ridiculous and now I'm starting to get confused. I really wish if people didn't know wtf they were talking about they wouldn't input or give advice on the procedure.

    So, I typically input the 404a as a liquid on the high pressure side at the king valve coming out of the receiver WITH the system running. Is this the correct method?

    I hear people say leave the system running, shut it off, throttle the 404 in the low pressure vapor side as a liquid, etc.

    What is the real procedure and BEST procedure when charging in a liquid state?

    And when would you ever want to charge the 404A on the low pressure side if ever?



  2. #2
    Join Date
    Feb 2010
    Location
    England
    Age
    59
    Posts
    243
    Rep Power
    16

    Re: 404a Charging CONFUSION

    Quote Originally Posted by ZeroTolerance View Post
    So, I typically input the 404a as a liquid on the high pressure side at the king valve coming out of the receiver WITH the system running. Is this the correct method?

    I hear people say leave the system running, shut it off, throttle the 404 in the low pressure vapor side as a liquid, etc.

    What is the real procedure and BEST procedure when charging in a liquid state?

    And when would you ever want to charge the 404A on the low pressure side if ever?

    What you are doing is fine, but it is only one of the ways to do it.

    It is not BS realy it is common sense.

    Put the refrigerant in the system anyway you want just do it in liquid form. (you could even do it in vapour form as long as you charge the whole cylinder)

    If that means weighing the whole charge into a reciever or into the liquid line with the reciever valve closed when running or throtled into the suction while running or even from an access point in the suction near the evaporator.

    It does not matter. It honestly doesn't

    What does matter is that you are comfortable doing it the way you do.

    coolrunnings

    .
    Last edited by cool runings; 09-05-2010 at 08:01 PM.

  3. #3
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: 404a Charging CONFUSION

    I heard though that when charging via liquid on the suction side it could and would damage the compressor? As liquids don't compress and BOOM there goes your compressor.

    So is the proper procedure to throttle it in while the system is running or while its off if doing it near the compressor on the suction side?

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: 404a Charging CONFUSION

    I would charge enough liquid to run the system into the reciever with the system off, then run it up and charge into the suction valve on the compressor, i would throttle the valve on the gauge manifold so that little or no liquid reached the suction valve on the compressor. Effectivly turning the gauges into a hand expansion valve.

    If you are not charging the whole bottle, so long as the refrigerant leaves the bottle as a liquid, it doesn't matter if it vapourises before reaching the system.

    And as Cool runnings says if you are putting the whole bottle into the one system you can charge as a vapour.

    Jon
    Last edited by monkey spanners; 09-05-2010 at 08:17 PM.

  5. #5
    Join Date
    Apr 2010
    Location
    USA
    Posts
    62
    Rep Power
    14

    Re: 404a Charging CONFUSION

    Quote Originally Posted by cool runings View Post
    What you are doing is fine, but it is only one of the ways to do it.

    It is not BS realy it is common sense.

    Put the refrigerant in the system anyway you want just do it in liquid form. (you could even do it in vapour form as long as you charge the whole cylinder)

    If that means weighing the whole charge into a reciever or into the liquid line with the reciever valve closed when running or throtled into the suction while running or even from an access point in the suction near the evaporator.

    It does not matter. It honestly doesn't

    What does matter is that you are comfortable doing it the way you do.

    coolrunnings

    .
    High side charging with the system running is not how you do it. You could pump your can full and explode it.

    Dumping liquid into to high side is a normal practice with the system off. As is metering liquid into the low side when it's running.
    What matters is safety.

  6. #6
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: 404a Charging CONFUSION

    "or into the liquid line with the reciever valve closed when running"

    Are you referring to putting the charging line on the output (king valve) of the receiver and shutting off the input (king valve) of the receiver and charge it while the system is running?

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: 404a Charging CONFUSION

    If you shut the input valve on the reciever you will just fill your condenser up with liquid and the unit will either, trip on the high pressure switch if fitted, the compressor will stall and trip a breaker, or there will be a loud bang. If there is a loud bang, don't worry, you won't hear it...

    Why not get yourself one of thoses charging metering devices which you fit on the bottle and it boils the liquid off as it goes through?

  8. #8
    Join Date
    May 2010
    Location
    Dallas
    Age
    39
    Posts
    41
    Rep Power
    0

    Re: 404a Charging CONFUSION

    Thanks for all the info; I am new to the game so please bare with me. I don't have a mentor/teacher to learn from, so I have been doing a lot of research on my own (online). I am a facilities manager and like to be hands on, so I try and do all the work the restaurants request myself without having to outsource.

  9. #9
    Join Date
    May 2010
    Location
    Odessa, TX
    Age
    55
    Posts
    9
    Rep Power
    0

    Re: 404a Charging CONFUSION

    If it is a system that holds a lot of refrigerant, and it is empty, then you should be in a vaccuum. So charging into the liquid line until the pressure equalize should not be a problem. Once the pressure equalizes, then start the unit and start metering in liquid into the low side.(meter it with your manifold and hoses). If the unit is very small, you can overcharge it before it even equalizes.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: 404a Charging CONFUSION

    You can also use a quick-charger like this one... (It seems somewhat expensive so please look around)

    http://www.professionalequipment.com...c-accessories/
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Mar 2008
    Location
    England
    Posts
    235
    Rep Power
    20

    Re: 404a Charging CONFUSION

    Quote Originally Posted by Brian_UK View Post
    You can also use a quick-charger like this one... (It seems somewhat expensive so please look around)

    http://www.professionalequipment.com...c-accessories/
    Been using the quick charge for many years, well worth the money, save you a lot of time and you don't have the risk of liquid slugging the compressor.

  12. #12
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: 404a Charging CONFUSION

    im going to have to get me one of those.. ive always just used a sight glass in the gauges and made sure i was evaporating in my manifold.. but is a pain as the pressure on the system changes...
    -Christopher

Similar Threads

  1. Liquid charging through the suction side
    By deu58 in forum Fundamentals
    Replies: 13
    Last Post: 02-07-2010, 05:23 AM
  2. Charging 404A into a new walk-in freezer
    By handyhusband01 in forum Commercial
    Replies: 17
    Last Post: 09-06-2010, 11:04 PM
  3. Why is suction gauge reading retard during charging?
    By acrefconsultant in forum Technical Discussions
    Replies: 10
    Last Post: 27-09-2009, 08:57 PM
  4. 18 seer AS charging problem,best way?
    By nagzul in forum Air Conditioning
    Replies: 3
    Last Post: 01-05-2008, 07:44 AM
  5. R 404a
    By Samarjit Sen in forum Refrigerants
    Replies: 59
    Last Post: 07-08-2007, 06:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •