    Product Load



    When working out the product load for a freezer is the following method correct-

    (SA x TD) + L + (SB X TD) x PW
    PD X 3.6
    Where-
    SA = sensible heat above freezing
    TD = Temperature above/below freezing
    L= LAtente heat
    SB= sensible below freezing
    PW= product weight
    PD = pull down period of product in hours

    By my recall the top line give me the load in kj/kg and by dividing it by the time give me an answer in watts.

    Please any information is greatly appreciated.



  2. #2
    Join Date
    May 2010
    Location
    Townsville
    Posts
    12
    Rep Power
    0

    Re: Product Load

    Quote Originally Posted by scottmax View Post
    When working out the product load for a freezer is the following method correct-

    (SA x TD) + L + (SB X TD) x PW
    PD X 3.6
    Where-
    SA = sensible heat above freezing
    TD = Temperature above/below freezing
    L= LAtente heat
    SB= sensible below freezing
    PW= product weight
    PD = pull down period of product in hours

    By my recall the top line give me the load in kj/kg and by dividing it by the time give me an answer in watts.

    Please any information is greatly appreciated.
    [QUOTE=scottmax;187373]When working out the product load for a freezer is the following method correct-

    (SA x TD) + L + (SB X TD) x PW
    PD X 3.6

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Product Load

    Change the 3.6 to 3600,

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Product Load

    Hi there,

    There is a problem with your equation :

    Product weight must be "Product weight loaded per day" and therefore; you must replace 3.6 with 86400 which is " 60x60x24

    cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    May 2010
    Location
    Townsville
    Posts
    12
    Rep Power
    0

    Re: Product Load

    Quote Originally Posted by Magoo View Post
    Change the 3.6 to 3600,

    What if my weight measurement is in kg's. Don't I have to divide both the top and bottom by 1000?

  6. #6
    Join Date
    May 2010
    Location
    Townsville
    Posts
    12
    Rep Power
    0

    Re: Product Load

    I am working out a load for a spiral freezer so I only need 1 hour for the time.

  7. #7
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Product Load

    Quote Originally Posted by scottmax View Post
    (SA x TD) + L + (SB X TD) x PW
    PD X 3.6
    Where-
    SA = sensible heat above freezing
    TD = Temperature above/below freezing
    L= LAtente heat
    SB= sensible below freezing
    PW= product weight
    PD = pull down period of product in hours

    By my recall the top line give me the load in kj/kg and by dividing it by the time give me an answer in watts.

    Please any information is greatly appreciated.
    There is a mistake, (SA x TD) + L also must multiplied by PW i.e. formula is to be:
    ((SA x TD) + L + (SB X TD))x PW
    PD X 3.6

    What if my weight measurement is in kg's. Don't I have to divide both the top and bottom by 1000?
    If Latente heat is in kJ/kg, sensible heat above/below in kJ/(kg*Cdeg), then result will be in W.
    Last edited by Aik; 08-05-2010 at 01:36 PM.
    In some places will have to think ...

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Product Load

    Hi scottmax.
    Specific heat values are expressed as Kj/Kg/ 'K, using the 3.6 factor gives answer in watts, and 3600 gives answer in Kw.
    For a spiral the pull down factor has to be expressed as hours or fraction of an hour if retention time in spiral is in minutes.
    Don't forget the base load with spiral, that is fans, drives and insulation. Also depending on production runs the evaporator size for snow/ice building is important as well. Add a safety factor on to refrig capacity as well. Retention time, air direction and velocity, belt coverage, sealed product or open product, thickness, cooked or raw, wet or dry. All things to be taken into account.
    Example : 750kg/ hour of fish product, retention 35 minutes, exit temp -18'C, fan Kw 30, refrig capacity 135Kw @ -40 evaporating +35 condensing.

    hope this helps. Magoo
    Last edited by Magoo; 09-05-2010 at 12:18 AM. Reason: addition

  9. #9
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Product Load

    If it is a repeated failure then it might be related to system processing/ charging. Slow vapor charging results in scroll failure after 3 to 4 months. Set the LP not less than 25 Psig. Flush out the system with N2 and charge 70% of the refrigerant in the vacuum then charge the balance in suction side while running.

  10. #10
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Product Load

    Please igore my previous reply.

  11. #11
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Product Load

    To clarify more, the correct equation for Product Load calculation should be :

    [(SA x TDa) + L + (SB X TDb)] xPW x SLF
    PDt X 3600

    where : SA & SB are Specific Heats, units are KJ
    Kg.deg.K

    : TDa = entering product temp. - product
    freezing temp. (deg.K)
    : TDb = product freezing temp. - final
    product temp. (deg.K)
    : PW = Prod. weight (Kg.)
    : SLF = Safety load factor(1.2),depends on
    your design considerations.
    : PDt = Pull down (hr.)

    After inputing all above parameters, your Product Load shall be in the Kilowatts unit.

    In Spiral Freezers heat load calculations, you have to consider many factors as what Magoo have said.

    goodluck..
    <"No one is so smart, they just stay with problems longer and use their imagination">

  12. #12
    Join Date
    May 2010
    Location
    Townsville
    Posts
    12
    Rep Power
    0

    Re: Product Load

    Thanks for the info.
    Would it be fair to say with the experience on this board that a core temp of around -3 C is achievable if I use my calculation to -10C exit temp?
    I am cooling small meat pies (its an Australian thing) that weigh around 220grams in total. There are going in nude directly on the belt. Entering @50C. I have worked out a Product Load of 142kW. We are cooling 5106p/hr
    The client will be happy with a core of -3 we will get the rest over the next 24 hours in the main freezer.

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Product Load

    Hi Scottmax,
    the core temp will drop after a short period after leaving spiral. The temp equibulates, ie evens out. Pies are a strange thing to freeze due to air gap under the lid of pie.
    You can reduce refrig load if you have space for an ambient cooler using fresh air to drop temp lower than +50'C after leaving the oven.
    Last edited by Magoo; 14-05-2010 at 01:25 AM. Reason: spelling

  14. #14
    Join Date
    May 2010
    Location
    Townsville
    Posts
    12
    Rep Power
    0

    Re: Product Load

    We have made allowance for ambient cooling but in summer up here 35 C is not uncommon. They are only able to stay in the ambient cooler for 35min max before they are shipped out and run through the spiral. They enter the ambient cooler @ approx 85 C and we are guestimating they will loose around 35K in this time. The ambient cooler will be force fed air via a mechanical means. This serves as a double purpose to feed oxygen to the oven also.

  15. #15
    Join Date
    May 2010
    Location
    KSA
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: Product Load

    Kool sharing

  16. #16
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Product Load

    Hi all
    firstly it is really good topic.

    I try to use it but I don't understand some things.
    Pls correct my mistakes

    I need 750 kg Lamb freezer in 8 hour. To find How many kw I need for freezing ?

    SA = I don't know
    TDa = 40 - (-18) = 58 C
    L = I don't know
    SB = I don't know
    TDb = -18C
    PW = 750
    SLF = 1.2

    Thanks for help



  17. #17
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Product Load

    Hi again I found all but can't find K ?
    What is L ?

  18. #18
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Product Load

    K is only a temp. unit meaning deg. Kelvin.
    L is the specific heat of the product at freezing temp. or more commonly known as Latent Heat of the product. L varies with product type and can be found on ref. design tables and charts.
    <"No one is so smart, they just stay with problems longer and use their imagination">

Similar Threads

  1. Blast Freezer Heat Load calculations
    By smpsmp45 in forum NH3
    Replies: 5
    Last Post: 03-04-2010, 10:20 PM
  2. Heat load calculations Help!
    By jbomba in forum Technical Speculations
    Replies: 7
    Last Post: 17-10-2009, 11:12 AM
  3. Product Load Calculation
    By boy in forum Commercial
    Replies: 4
    Last Post: 12-08-2008, 02:50 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •