    What its horse power LRA = 49 and LRA = 58



    Please help.

    I gonna change window type aircoditioner the BTU is 24,000 and 18,000 and i have compressor LRA = 49 and LRA= 58. What is horsepower of that compressor. What LRA i will use in 24,000 BTU,
    What number of microfarrad ( uf ) of capacitor i will use in 2 compressor.

    How can i know the horsepower of window type aircon, in BTU, kj, Ampere, Watts, Ton.



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by pinoyako View Post
    Please help.

    I gonna change window type aircoditioner the BTU is 24,000 and 18,000 and i have compressor LRA = 49 and LRA= 58. What is horsepower of that compressor. What LRA i will use in 24,000 BTU,
    What number of microfarrad ( uf ) of capacitor i will use in 2 compressor.

    How can i know the horsepower of window type aircon, in BTU, kj, Ampere, Watts, Ton.
    Hi in order to calculate please give some info on voltage ,this is an important factor and of course no' of phases!!u should know that most units have a name plate on the back or front with all the energy ratings.
    Last edited by goshen; 07-05-2010 at 12:51 PM.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: What its horse power LRA = 49 and LRA = 58

    LRA = Locked Rotor Amperes.

    18000 BTU is 2 HP
    24000 BTU is 2.5 HP

    for the firs one 40mf
    for the second 50mf

    you can tell the capacity of the compressor from the model number.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by chemi-cool View Post
    LRA = Locked Rotor Amperes.

    18000 BTU is 2 HP
    24000 BTU is 2.5 HP

    for the firs one 40mf
    for the second 50mf

    you can tell the capacity of the compressor from the model number.
    Hi :
    12000btu=1tr
    and hp is by rule of thumb approximtly as quoted
    but calculating watts and amps is directly voltage related!!
    i think u will like this one :
    http://www.mhi-inc.com/Converter/watt_calculator.htm

    http://www.sengpielaudio.com/calculator-ohm.htm
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    May 2010
    Location
    phillippines
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by goshen View Post
    Hi in order to calculate please give some info on voltage ,this is an important factor and of course no' of phases!!u should know that most units have a name plate on the back or front with all the energy ratings.
    220 volts, single phase, what Compressor LRA will i use in 24,000 BTU,

    LRA =49 or LRA=58.

  6. #6
    Join Date
    May 2010
    Location
    phillippines
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by chemi-cool View Post
    LRA = Locked Rotor Amperes.

    18000 BTU is 2 HP
    24000 BTU is 2.5 HP

    for the firs one 40mf
    for the second 50mf

    you can tell the capacity of the compressor from the model number.
    Please where is the website that i will visit to see the compressor capacity by its model.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by pinoyako View Post
    Please where is the website that i will visit to see the compressor capacity by its model.
    Give me the compressor model and I will direct you to the right place.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: What its horse power LRA = 49 and LRA = 58

    When you changing compressor, try to stick with original one by model number. If you cannot, than you need to find displacement of original compressor to find replacement one with same pumping capacity. Or, you need to find capacity of original compressor at some standard condition like ASHRAE for AC (7,2°C evaporation and 54,4°C for condensation temperatures) and find replacement with same capacity at SAME conditions.
    Horsepower (in cooling capacity) is of not much practical use here because of rounding practice. Since window type AC have usually capillary tube as expansion device it is essential (for proper work and compressor longevity) that compressor have as much as close capacity (at same conditions) or displacement.
    Last edited by nike123; 08-05-2010 at 07:22 AM.

  9. #9
    Join Date
    May 2010
    Location
    phillippines
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by chemi-cool View Post
    Give me the compressor model and I will direct you to the right place.
    Panasonic
    2k34s3r
    236a
    6a
    58 lra

    Matsu****a
    2k28s3r
    236a
    6a
    49 lra

    That is compressor i had, for what BTU capacity is for that 2 compressor

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: What its horse power LRA = 49 and LRA = 58

    all the info you need is here, good luck.
    http://www.panasonic.com/industrial/.../k-series.aspx

  11. #11
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: What its horse power LRA = 49 and LRA = 58

    Hi there i usually dont choose a comp by lra, but by nominal current in your case ,220v 24000btu would be approx 8 amps = 56 lra ,but as mentioned above ,a compressor should be replaced by the same make and model
    this will save u time in instalation and running.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  12. #12
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by goshen View Post
    Hi there i usually dont choose a comp by lra, but by nominal current in your case ,220v 24000btu would be approx 8 amps = 56 lra ,but as mentioned above ,a compressor should be replaced by the same make and model
    this will save u time in instalation and running.
    If you know LRA, you can find out exact running ampere.if LRA 56 Then 56*100/500=11.2A.

    Moideen-dubai

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by moideen View Post
    If you know LRA, you can find out exact running ampere.if LRA 56 Then 56*100/500=11.2A.

    Moideen-dubai
    Not exactly! Running current depend on compressor compression ratio and state of mechanical parts. These changes, but LRA is always same.
    We have LRA => 5 to 7*FLA
    FLA => Fixed number
    Running amperes => lower than FLA

    Do not compare compressors by amperage.
    Only correct is:

    1. By displacement and same area of application (LT,MT,HT,AC)
    2. By same capacity at SAME RATED conditions and same area of application (LT,MT,HT,AC)
    Last edited by nike123; 13-05-2010 at 08:13 AM.

  14. #14
    Join Date
    May 2010
    Location
    Odessa, TX
    Age
    55
    Posts
    9
    Rep Power
    0

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by moideen View Post
    If you know LRA, you can find out exact running ampere.if LRA 56 Then 56*100/500=11.2A.

    Moideen-dubai
    A really easy way to calculate the ball park of rla/fla is to divide LRA by 5. 56/5=11.2 Most motors lra is five times higher than its rla/fla, but can be as high as 7 times higher.

  15. #15
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: What its horse power LRA = 49 and LRA = 58

    Quote Originally Posted by surenuff View Post
    A really easy way to calculate the ball park of rla/fla is to divide LRA by 5. 56/5=11.2 Most motors lra is five times higher than its rla/fla, but can be as high as 7 times higher.
    Hi i think we would all agreee that the best way is to read the amps stated on the nameplate itself.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  16. #16
    Join Date
    Mar 2010
    Location
    pakistan
    Posts
    44
    Rep Power
    0

    Re: What its horse power LRA = 49 and LRA = 58

    from where u takin the 56*100/500 and for other amirs plz give me the said mathod