07-05-2010, 04:06 AM #1
chiller evap size for daikin 37kw compressor
hallo friend....
can anyone help me how to calculate evap and water cooler condensor size for chiller....
secondary fluid (water) details.
inlet water temp=25degc
outlet water temp=15degc
water flow rate=22 lpm
it is possible 1 unit 37kw daikin compressor can handle this???
thanks...
-
07-05-2010, 06:27 AM #2
-
07-05-2010, 10:29 AM #3
Re: chiller evap size for daikin 37kw compressor
thanks for reply. 15.54kw means cooling capacity??
one more question is if i have a 37kw daikin compressor, the cooling capacity??
-
07-05-2010, 10:48 AM #4
Re: chiller evap size for daikin 37kw compressor
In some places will have to think ...
-
07-05-2010, 11:15 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: chiller evap size for daikin 37kw compressor
Chiller water Δt should be 5K for proper chiller operation and best heat transfer at water to refrigerant heat exchanger.
Therefore, for your 37kW cooling capacity, water flow at evaporator should be ~106L/min or 6,4 m^3/hr.
If your process require higher Δt and different flow rate, you should use mixing valve or hydraulic separator.
Where and how did you got these data you present us here?
With flow and capacity what you posted, Δt would be 24K.Last edited by nike123; 07-05-2010 at 11:28 AM.
-
07-05-2010, 12:12 PM #6
Re: chiller evap size for daikin 37kw compressor
If you need to chill water from 25 C to 15 C you must take compressor with proper capacity ( 15.54 kW or no much more). Evaporating temperature would be near 7-10 C.
If you have compressor with capacity of 37 kW at 7-10 C evaporating temperature it would be done capacity regulation, otherwise evaporating temperature would be much lower and would be big problems...In some places will have to think ...
-
07-05-2010, 03:49 PM #7
Re: chiller evap size for daikin 37kw compressor
ok....thanks both of u..
i put wrong people on design and installation chiller in my work place, now i have to pay the price to study and correct it... actually i m electrical automation specialist.
-
07-05-2010, 03:55 PM #8
Re: chiller evap size for daikin 37kw compressor
or i can unload the compressor maybe 50% or 25% load when reach the set point.
-
07-05-2010, 06:49 PM #9
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: chiller evap size for daikin 37kw compressor
Running unloaded for long periods mean bad oil return and inefficient work.
Install buffer tank/hydraulic separator in one tank
http://www.cemline.com/products/steeltank/sebmenu.asp
and use dedicated pumps for primary and secondary circuit.
Also, you could calculate tank capacity here according to minimal running time of 10 min for chiller.
-
07-05-2010, 07:17 PM #10
Re: chiller evap size for daikin 37kw compressor
If use tank capacity, then you may use compressor of 37 kW capacity and system will work without any problems (compressor's working time will be shorter).
In some places will have to think ...
-
08-05-2010, 09:19 AM #11
Re: chiller evap size for daikin 37kw compressor
any idea from ur if i just install copper pipe after expansion device as evap in the chill water tank, the calculation for evap piping surface for my 37kw compressor.....thanks again...
-
08-05-2010, 11:48 AM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: chiller evap size for daikin 37kw compressor
-
09-05-2010, 04:20 PM #13
Re: chiller evap size for daikin 37kw compressor
ok,i can put a lot of pipe, make it paraller circuit, like water chiller evap. of course the water in tank move all the time. i have interest in this field.this is my 2nd project. the 1st project i had completed very successfully to installation ***** r22 bitzer osn7471-k with eco,the result is -45degc...
-
09-05-2010, 06:15 PM #14
-
11-05-2010, 03:38 AM #15
Re: chiller evap size for daikin 37kw compressor
sure, can u find me a solution???
Similar Threads
-
mcquay centrifugal chiller 063 compressor
By maico in forum Trouble ShootingReplies: 4Last Post: 22-11-2010, 06:40 PM -
copeland compressor btu @ 20degree evap.
By skyking in forum Technical SpeculationsReplies: 6Last Post: 03-09-2009, 09:45 AM -
compressor / electrical problem
By Northdude in forum CommercialReplies: 6Last Post: 17-01-2009, 10:24 AM -
started to make an evap for my chiller
By The MG Pony in forum FundamentalsReplies: 8Last Post: 22-07-2006, 08:44 PM -
Chiller coldroom compressor problems.
By Lucas in forum Trouble ShootingReplies: 27Last Post: 24-12-2004, 11:30 AM