    chiller evap size for daikin 37kw compressor



    hallo friend....
    can anyone help me how to calculate evap and water cooler condensor size for chiller....

    secondary fluid (water) details.
    inlet water temp=25degc
    outlet water temp=15degc
    water flow rate=22 lpm

    it is possible 1 unit 37kw daikin compressor can handle this???
    thanks...



  2. #2
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller evap size for daikin 37kw compressor

    Quote Originally Posted by ah fai View Post
    hallo friend....
    can anyone help me how to calculate evap and water cooler condensor size for chiller....

    secondary fluid (water) details.
    inlet water temp=25degc
    outlet water temp=15degc
    water flow rate=22 lpm

    it is possible 1 unit 37kw daikin compressor can handle this???
    thanks...
    If water flow rate = 22 lpm (litre per minute) then:
    G=22 l/m=0.37*10^(-3) m^3/s=0.37 kg/s (density of water is 1000 kg/m^3)
    Q=c*G*(Tin-Tout)=4200 J/(kg*degc)*0.37 kg/s * (25 degc- 15degc)= 15.54 kJ/s=15.54 kW

  3. #3
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller evap size for daikin 37kw compressor

    thanks for reply. 15.54kw means cooling capacity??
    one more question is if i have a 37kw daikin compressor, the cooling capacity??

  4. #4
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller evap size for daikin 37kw compressor

    Quote Originally Posted by ah fai View Post
    thanks for reply. 15.54kw means cooling capacity??
    one more question is if i have a 37kw daikin compressor, the cooling capacity??
    Yes, it's a cooling capacity.
    Really, I don't understand the 2-nd part of your question. What mark of compressor, evaporating/condensing temperature, type of refrigerant? Capacity of compressor depends on thise parameters...
    In some places will have to think ...

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller evap size for daikin 37kw compressor

    Chiller water Δt should be 5K for proper chiller operation and best heat transfer at water to refrigerant heat exchanger.
    Therefore, for your 37kW cooling capacity, water flow at evaporator should be ~106L/min or 6,4 m^3/hr.
    If your process require higher Δt and different flow rate, you should use mixing valve or hydraulic separator.

    Where and how did you got these data you present us here?
    With flow and capacity what you posted, Δt would be 24K.
    Last edited by nike123; 07-05-2010 at 11:28 AM.

  6. #6
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller evap size for daikin 37kw compressor

    If you need to chill water from 25 C to 15 C you must take compressor with proper capacity ( 15.54 kW or no much more). Evaporating temperature would be near 7-10 C.
    If you have compressor with capacity of 37 kW at 7-10 C evaporating temperature it would be done capacity regulation, otherwise evaporating temperature would be much lower and would be big problems...
    In some places will have to think ...

  7. #7
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller evap size for daikin 37kw compressor

    ok....thanks both of u..
    i put wrong people on design and installation chiller in my work place, now i have to pay the price to study and correct it... actually i m electrical automation specialist.

  8. #8
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller evap size for daikin 37kw compressor

    or i can unload the compressor maybe 50% or 25% load when reach the set point.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller evap size for daikin 37kw compressor

    Quote Originally Posted by ah fai View Post
    or i can unload the compressor maybe 50% or 25% load when reach the set point.
    Running unloaded for long periods mean bad oil return and inefficient work.

    Install buffer tank/hydraulic separator in one tank
    http://www.cemline.com/products/steeltank/sebmenu.asp


    and use dedicated pumps for primary and secondary circuit.
    Also, you could calculate tank capacity here according to minimal running time of 10 min for chiller.

  10. #10
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller evap size for daikin 37kw compressor

    If use tank capacity, then you may use compressor of 37 kW capacity and system will work without any problems (compressor's working time will be shorter).
    In some places will have to think ...

  11. #11
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller evap size for daikin 37kw compressor

    any idea from ur if i just install copper pipe after expansion device as evap in the chill water tank, the calculation for evap piping surface for my 37kw compressor.....thanks again...

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: chiller evap size for daikin 37kw compressor

    Quote Originally Posted by ah fai View Post
    any idea from ur if i just install copper pipe after expansion device as evap in the chill water tank, the calculation for evap piping surface for my 37kw compressor.....thanks again...
    Not good. One pipe mean big pressure drop. Also, liquid in tank need to be moved or you could freeze it quickly. You need BPHE (brazed plate heat exchanger ) and correct pump for right flow.

    Why don't you find some contractor to do proper job for you?

  13. #13
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller evap size for daikin 37kw compressor

    ok,i can put a lot of pipe, make it paraller circuit, like water chiller evap. of course the water in tank move all the time. i have interest in this field.this is my 2nd project. the 1st project i had completed very successfully to installation ***** r22 bitzer osn7471-k with eco,the result is -45degc...

  14. #14
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: chiller evap size for daikin 37kw compressor

    Quote Originally Posted by ah fai View Post
    ok,i can put a lot of pipe, make it paraller circuit, like water chiller evap. of course the water in tank move all the time. i have interest in this field.
    You can do it and your's the next post will be: how calculate evaporator capacity of pipe situated in tank in which continually move water.
    In some places will have to think ...

  15. #15
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller evap size for daikin 37kw compressor

    sure, can u find me a solution???

Similar Threads

  1. mcquay centrifugal chiller 063 compressor
    By maico in forum Trouble Shooting
    Replies: 4
    Last Post: 22-11-2010, 06:40 PM
  2. copeland compressor btu @ 20degree evap.
    By skyking in forum Technical Speculations
    Replies: 6
    Last Post: 03-09-2009, 09:45 AM
  3. compressor / electrical problem
    By Northdude in forum Commercial
    Replies: 6
    Last Post: 17-01-2009, 10:24 AM
  4. started to make an evap for my chiller
    By The MG Pony in forum Fundamentals
    Replies: 8
    Last Post: 22-07-2006, 08:44 PM
  5. Chiller coldroom compressor problems.
    By Lucas in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2004, 11:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •