Thread: Evaporator Fan Heat Load
05-05-2010, 10:42 PM #1
How can we find out evap fan heat load? Is it the total kWe of fans that is added directly to the total load or its the % of total load that is added after finding to final load?
In case of VSD fans, how this load would vary or be considered?
regardsLast edited by GBRD; 06-05-2010 at 02:03 AM. Reason: correcting data
BR
06-05-2010, 04:24 AM #2
Re: Evaporator Fan Heat Load
try ringing the manufacturer or get some data sheets?
06-05-2010, 05:09 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Go with power input of motor!
http://www.engineeringtoolbox.com/el...ain-d_707.htmlLast edited by nike123; 06-05-2010 at 05:11 AM.
06-05-2010, 05:51 AM #4
As nike123 said go for the drawn power, or else the rated full load amps of motor, to have a safety margin built in.
Magoo
06-05-2010, 07:10 AM #5
Thanks Nike123 & Magoo. Do you mean -
kWr = Motor kWe x No. of motors x No. of running hrs ??
If above is correct, how about the efficiency of motors? Should this be considered at all?BR
06-05-2010, 08:08 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
06-05-2010, 11:57 PM #7
Thank you all of you..
BR
Blast Freezer Heat Load calculations
By smpsmp45 in forum NH3Replies: 5Last Post: 03-04-2010, 10:20 PM -
Basics or is it?
By Fett in forum FundamentalsReplies: 17Last Post: 10-09-2009, 01:45 AM -
Heat transfer coefficient - Coolpack
By Graham in forum FundamentalsReplies: 10Last Post: 28-05-2008, 01:08 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM