    Capillary systems



    Hi,
    I have always been taught and led to believe that on a capillary system, the Mass flow rate of the compressor MUST be equivalent to the capillary capactiy.
    So in the case of compressor failure, it must be replaced with a compressor of the exact same pumping capacity. Or a new compressor and new capillary must be installed that match eachother.

    My boss has constantly replaced compressors on capillary systems, with different compressors with different pumping capacities and different 'fully loaded amp' ratings, and says it can be easily fixed by playing with gas levels.

    Is this correct?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Capillary systems

    Hi Young gun,

    The compressor should be the same or equivalent to what was on there originally if you want the system to work as the manufacturers intended.

    Jon

  3. #3
    Join Date
    Sep 2008
    Location
    USA, Phx, Az
    Age
    38
    Posts
    89
    Rep Power
    16

    Re: Capillary systems

    A capillary tube is just a metering device. If you install a compressor slightly bigger than the one that was on the system originally. Assume you recharge the system with the same amount of gas. You're high side pressure should be slightly higher than it would have been with the previous compressor.

    A bigger compressor will force the gas through the cap. tube. In my experience it is good practice to replace a compressor with original equipment. What your boss is doing is okay but I would consider it not Kosher and should only be done when original equipment is un-obtainable.

    -Fett

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Capillary systems

    Quote Originally Posted by young gun View Post
    Hi,
    I have always been taught and led to believe that on a capillary system, the Mass flow rate of the compressor MUST be equivalent to the capillary capactiy.
    You have been well taught!

Similar Threads

  1. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  4. Superheat in Capillary tube systems
    By setrite in forum Technical Speculations
    Replies: 3
    Last Post: 20-06-2002, 12:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •