Dry Nitrogen. Found 2 leaks (phos brazed joints where I couldn't see - rookie mistakes). Repaired. Soap tested all joints again. Pressurized to 140 psi using nitrogen and the gage held there for 3 days. If the sun was on the compressor unit the pressure rose to 148psi. Cooled at night - pressure back to 140.