    Qeustion ,I have 150 screw york chiller kicking out on (lep) Brine .Any one have a suggestion of the problem. thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: randyc777

    Take your pick.
    Low system pressure.. short of refrigerant.
    Poor flow through the evap.. blocked shell and tube or strainer.
    Brine mix wrong.
    Liquid line filter blocked or part blocked.
    Expansion valve hunting.
    LWT probe faulty reading. driving the LWT to low. Causing LP cut outs.
    LP Pressure transducer faulty..
    Just a few for starters.
    A bit more info would be nice!
    Grizzly