blast freezer
could anybody tell me anything about i want to make blast freezer with condensing unit hsn 7471-75
-
04-05-2010, 07:31 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: blast freezer
Blast freezer construction doesn't start with condensing unit. It finishes with it.
-
05-05-2010, 05:25 PM #3
Re: blast freezer
more info needed,what size the room what type of product what is the temperature of the product,basically the heat load,ambient etc.
-
08-05-2010, 12:43 PM #4
Re: blast freezer
HSN7471-75 is a Bitzer Semi Hermetic Screw Compressor. You still need an evaporator, condenser and all the necessary equipment and controls to make it work.
This compressor can give 44.4 Kw at -45 Deg. C suction and 40 Deg. C Condensing with R 507A, based on 10 K suction superheat and liquid subcooling.
So, you should be able to pull down 12000 kg of Sardines from 12 Deg. C to -25 Deg. C core temperature in about 14 hours.
Freezer room size should be approximately 5 X 4 X 3.2 meter high to accommodate product and evaporator, with neccessary fans and false ceilingI am not always right, but I'm never wrong!
Similar Threads
-
Air blast freezer designation - limited space
By Sien in forum IndustrialReplies: 5Last Post: 14-12-2009, 10:13 AM -
Blast Freezer Within Freezer
By rickmor in forum Technical DiscussionsReplies: 4Last Post: 18-06-2009, 03:37 AM -
Trolley freezer & blast freezer
By smpsmp45 in forum NH3Replies: 0Last Post: 25-08-2007, 07:29 AM -
Blast Freezer
By w.l.ong in forum IndustrialReplies: 17Last Post: 16-12-2006, 10:34 AM -
Blast Freezer Questions
By rickmor in forum IndustrialReplies: 2Last Post: 11-04-2006, 08:15 PM