DesA,
speaking to the receiver above the condenser discussion. The delta P to drive liquid up to receiver could be an advantage, so as to introduce more heat to system, penalty being the COP. From memory 2.3 foot head equas 1 Psig, and then apply the specific density factor for refrigerant. So long as the piping is trapped out of condenser and before the receiver.
Generally with ammonia plants the discharge pressure is applied to top of receiver as well, with the condenser above the receiver. Mainly because of the specifc density of ammonia being lighter than anything else, and to get the gravity transfer factor back to the receiver.
-
04-05-2010, 06:13 AM #2
Re: Condenser Puzzle
Thanks Magoo.
Could you perhaps expand this a bit further?
From memory 2.3 foot head equas 1 Psig, and then apply the specific density factor for refrigerant. So long as the piping is trapped out of condenser and before the receiver.
Generally with ammonia plants the discharge pressure is applied to top of receiver as well, with the condenser above the receiver. Mainly because of the specifc density of ammonia being lighter than anything else, and to get the gravity transfer factor back to the receiver.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
04-05-2010, 04:59 PM #3
Re: Condenser Puzzle
The lift being far less than 2.3ft, the effect upon head pressure would be far less than 1 psig... and this assumes lifting a solid column of liquid which is not necessarily the case. A vapor/liquid mixture would further reduce the effect upon head pressure... perhaps to the point where it is relatively inconsequential.
-
04-05-2010, 05:37 PM #4
Re: Condenser Puzzle
How sure are we of this, in practice though? Are there practical examples in the field where we can draw comparisons? Has anyone examples of a vertical filter-drier positioned at a level above the condenser outlet?
A condenser, as I understand things, can actually develop a reduced pressure as the vapour is condensed internally. This would be compounded as the liquid rains down. The effect of an induced back-pressure, with possible vapour-liquid pulsing/slugging is not well understood, at least in my head.
I'd love to be able to see inside the condenser-pipe-filter-drier combo.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
04-05-2010, 05:55 PM #5
Re: Condenser Puzzle
-
04-05-2010, 06:17 PM #6
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Parallel condensers Shell and tube paralle with Evaporative Condenser
By Herschmidt in forum NH3Replies: 2Last Post: 08-06-2010, 11:12 PM -
Problem with plugged condenser
By kurt s in forum FundamentalsReplies: 7Last Post: 02-10-2008, 06:46 PM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM -
Plate Heat Exchagers - Condenser
By Billy Ray in forum Technical DiscussionsReplies: 9Last Post: 11-05-2008, 06:16 PM