    Re: Condenser Puzzle

    Let's take this a step further:

    If there were a restriction in the body of the condenser, the reduced flow of chilled refrigerant would quickly equalize with the incoming water temp, making the exit refrigerant temp equal to the incoming water temp... therefore, the restriction is at (or very near) the exit.