    Condenser Puzzle



    Here's an odd problem:

    On a water cooled condenser, the temperature of the refrigerant leaving the condenser is lower than the temperature of the water entering the condenser.

    What could be the problem?



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Condenser Puzzle

    is there a pilot receiver on the system?

    if so, possibly pilot valve stuck in open position
    -Cheers-

    Tycho

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by Tycho View Post
    is there a pilot receiver on the system?

    if so, possibly pilot valve stuck in open position
    Nope... no pilot receiver. Assume a simple water cooled A/C system with TXV.

    But if there were a pilot receiver, how could that cause the refrigerant exit temp to drop below the water inlet temp?
    Last edited by Gary; 03-05-2010 at 08:18 PM.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condenser Puzzle

    Some restriction inside the condenser makes part of it work like evaporator.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by chemi-cool View Post
    Some restriction inside the condenser makes part of it work like evaporator.
    I agree.

    Are there any other possible causes?

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Condenser Puzzle

    Faulty thermometer

    Jon

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by monkey spanners View Post
    Faulty thermometer

    Jon
    Nope... sensors have been checked and are accurate.

    Any other possibilities?

  8. #8
    Join Date
    Nov 2007
    Location
    US
    Posts
    5
    Rep Power
    0

    Re: Condenser Puzzle

    Quote Originally Posted by chemi-cool View Post
    Some restriction inside the condenser makes part of it work like evaporator.
    I concur this restriction inside condenser answer. Otherwise, it doesn't make thermodynamics sense.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    The condenser is a PHE. Does that change anyone's opinion?

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Condenser Puzzle

    Is this question related with Alfa Laval book?

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by nike123 View Post
    Is this question related with Alfa Laval book?
    Could be...

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Let's take this a step further:

    If there were a restriction in the body of the condenser, the reduced flow of chilled refrigerant would quickly equalize with the incoming water temp, making the exit refrigerant temp equal to the incoming water temp... therefore, the restriction is at (or very near) the exit.
    Last edited by Gary; 03-05-2010 at 09:32 PM.

  13. #13
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Condenser Puzzle

    hey gary. give us a clue, whats the ambiant ?

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by sedgy View Post
    hey gary. give us a clue, whats the ambiant ?
    An excellent question, to which I do not know the answer, however the PHE is insulated as is the piping and sensors.

  15. #15
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Condenser Puzzle

    Its piped up backwards, so its feeding in the bottom and condensing, and has mostly filled with liquid, which is now boiling off to get out again...

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    It would still take a sudden pressure drop (restriction) to cause it to boil off and drop the temp.

  17. #17
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condenser Puzzle

    Orifice tube installed as for an evaporator, and PHE installed as a condenser by mistake.
    magoo

  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by Magoo View Post
    Orifice tube installed as for an evaporator, and PHE installed as a condenser by mistake.
    magoo
    Hmmm... orifice at the exit... I like it... seems unlikely... but imaginative. I've seen stranger things.

  19. #19
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condenser Puzzle

    Hi Gary.
    You can see if orifice tube is installed by the reducer as it is not the regular size, and some manufactures dimple to tube to orientate the position of the linear slot relative to the feed to PHE when applied as an evaporator.
    Talking about strange things, I had a water chiller that would not perform at all, and the problem was the TX valves two of, were welded in the wrong way around, and that was from the factory after all the quality control garbage.
    Weird things do happen

  20. #20
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Quote Originally Posted by nike123 View Post
    Is this question related with Alfa Laval book?
    Hypothetically: What if the condenser exit piping were looped upwards, then over, down through a filter drier? (This is common received knowledge in regards to filter-drier orientation & placement, it seems).

    Let's assume that, for argument, the level of the filter-drier were around 20% from the top of the PHE?

    Does this filter-drier operate like a 'through liquid receiver'?

    Where does the liquid level sit in the condenser, under such an arrangement?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  21. #21
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condenser Puzzle

    Des A
    you are in the wrong post.
    magoo

  22. #22
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Quote Originally Posted by Magoo View Post
    Des A
    you are in the wrong post.
    magoo
    No, I'm in the correct thread.

    The question stands. I'm following on from Nike's lead regarding the potential link between receiver location and condenser discharge temperature (the alfa laval book).

    This is the correct status of the application mentioned in the OP - not all facts were provided in order for the members to determine the cause-&-effect process. This led everyone to the 'restriction' conclusion - perhaps a little prematurely, in my view.
    Last edited by desA; 04-05-2010 at 04:03 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  23. #23
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    As Nike correctly guessed, this is the same system we were discussing in the other thread.

    The refrigerant exits the condenser at the bottom, loops upwards towards the top of the condenser, then down through the filter/drier.

    So this bring up two questions:

    1. Can this arrangement cause liquid to back up into the condenser?

    2. Can such a liquid backup cause the condenser exit temp to drop below the incoming water temp?
    Last edited by Gary; 04-05-2010 at 04:43 AM.

  24. #24
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    I see Chef lurking on the thread.

    I'd really value your insights on the filter-drier as 'gas bubbler' theory you proposed a few months back. What would its effect be on the condenser performance?

    At the root of this is the conventional logic which says that a filter-drier needs to oriented vertically downwards to act as a small accumulator, rather than lie horizontally. This comment has been raised many times on RE. Experimental results would tend to show that this orientation can have unconsidered consequences.

    I'd like to know more about the gas/liquid dynamics between condenser & filter-drier - what is really going on in that part of the system?

    As part of this, the condensation dynamics in a vertically-oriented PHE need to be well understood, especially in regards to the effect of excessive back-pressure, or imposed liquid trap level.
    Last edited by desA; 04-05-2010 at 04:50 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  25. #25
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condenser Puzzle

    DesA
    I hummmmmmmmmbly apologise. Oh great and wise person.
    magoo

  26. #26
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Quote Originally Posted by Magoo View Post
    DesA
    I hummmmmmmmmbly apologise. Oh great and wise person.
    magoo
    Hahah...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  27. #27
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condenser Puzzle

    Hi Gary.
    so now the posts are intergrated, that is a new twist.

  28. #28
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condenser Puzzle

    DesA,
    speaking to the receiver above the condenser discussion. The delta P to drive liquid up to receiver could be an advantage, so as to introduce more heat to system, penalty being the COP. From memory 2.3 foot head equas 1 Psig, and then apply the specific density factor for refrigerant. So long as the piping is trapped out of condenser and before the receiver.
    Generally with ammonia plants the discharge pressure is applied to top of receiver as well, with the condenser above the receiver. Mainly because of the specifc density of ammonia being lighter than anything else, and to get the gravity transfer factor back to the receiver.

  29. #29
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Thanks Magoo.

    Quote Originally Posted by Magoo View Post
    DesA,
    speaking to the receiver above the condenser discussion. The delta P to drive liquid up to receiver could be an advantage, so as to introduce more heat to system, penalty being the COP.
    Could you perhaps expand this a bit further?

    From memory 2.3 foot head equas 1 Psig, and then apply the specific density factor for refrigerant. So long as the piping is trapped out of condenser and before the receiver.
    What would this trap look like?

    Generally with ammonia plants the discharge pressure is applied to top of receiver as well, with the condenser above the receiver. Mainly because of the specifc density of ammonia being lighter than anything else, and to get the gravity transfer factor back to the receiver.
    Ok, understand this. Thanks very much.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  30. #30
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Condenser Puzzle

    Quote Originally Posted by desA View Post
    Hypothetically: What if the condenser exit piping were looped upwards, then over, down through a filter drier? (This is common received knowledge in regards to filter-drier orientation & placement, it seems).

    Let's assume that, for argument, the level of the filter-drier were around 20% from the top of the PHE?

    Does this filter-drier operate like a 'through liquid receiver'?

    Where does the liquid level sit in the condenser, under such an arrangement?

    I am not that good to answer your questions. I simply added 2 an2 and concluded that Gary possibly throw us bite to catch on this interesting matter, after he little "surfed" that Alfa Laval book.

  31. #31
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Wondered about your detective work.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  32. #32
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Condenser Puzzle

    It may be that the velocity in a PHE is quite high so the refrigerant cools to close to the liquid coolant temperature but has a high kinetic energy. When this reforms to normal pipe flow the kinetic energy is converted to static pressure. If it is an adiabatic process it would manifest itself as subcooling but if it were non adiabatic it may show up as colder refrigerant.

    However there does not seem to be a process where the refrigerant is colder than the liquid coolant unless there is a Joule Thompson expansion just before the pressure conversion back to static pressure.

    Chef

  33. #33
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Thanks very much for your thoughts, Chef - much appreciated.

    I'll tell you my thought processes:
    1. Filter-drier located high up condenser;
    2. Condensate backs up inside condenser;
    3. This raises operating pressure (Tc,sat);
    4. Condensate flow out discharge, up & over into filter-drier;
    5. Vapour-liquid separation, some level of vapour locking in upper bend;
    6. Expect process to be slightly erratic, with a small level of surging (nothing undue noticed in pressure gauges);
    7. Sub-cooled boiling occurs in condensate - bubbles rise upwards.

    The amount of excess sub-cooling begins very small at startup, but rises to around 6.5K towards the hot part of the cycle, as the liquid line heats up. This would correspond to more reactivity of the refrigerant - tendency to flash.

    We have to always bear in mind that we are dealing with 2-phase phenomena here, & that kinetic energy to static pressure conversion will be a little less simple.

    Physically, an exact replica of the same cycle, except for filter-drier position, runs as per expectation. The condenser is manufacturer-supplied with refrigerant stubs brazed & tested by them. It is one of the leading brands. I do not expect an exit blockage - although, it could always be argued so. (I will cut this line open & rebuild the pipework, to test the standard case.)

    I have strong suspicions that the 'pat' answer we often provide with respect to willy-nilly having a filter drier set vertically with flow downwards, without taking care with respect to location & relative height, may not be entirely valid. It is perhaps something to think more deeply about.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  34. #34
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by Magoo View Post
    DesA,
    speaking to the receiver above the condenser discussion. The delta P to drive liquid up to receiver could be an advantage, so as to introduce more heat to system, penalty being the COP. From memory 2.3 foot head equas 1 Psig, and then apply the specific density factor for refrigerant.
    The lift being far less than 2.3ft, the effect upon head pressure would be far less than 1 psig... and this assumes lifting a solid column of liquid which is not necessarily the case. A vapor/liquid mixture would further reduce the effect upon head pressure... perhaps to the point where it is relatively inconsequential.

  35. #35
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by Chef View Post
    However there does not seem to be a process where the refrigerant is colder than the liquid coolant unless there is a Joule Thompson expansion just before the pressure conversion back to static pressure.

    Chef
    If I understand you correctly:

    Joule Thompson expansion just before the pressure conversion back to static pressure = restriction at the exit

  36. #36
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Quote Originally Posted by Gary View Post
    The lift being far less than 2.3ft, the effect upon head pressure would be far less than 1 psig... and this assumes lifting a solid column of liquid which is not necessarily the case. A vapor/liquid mixture would further reduce the effect upon head pressure... perhaps to the point where it is relatively inconsequential.
    How sure are we of this, in practice though? Are there practical examples in the field where we can draw comparisons? Has anyone examples of a vertical filter-drier positioned at a level above the condenser outlet?

    A condenser, as I understand things, can actually develop a reduced pressure as the vapour is condensed internally. This would be compounded as the liquid rains down. The effect of an induced back-pressure, with possible vapour-liquid pulsing/slugging is not well understood, at least in my head.

    I'd love to be able to see inside the condenser-pipe-filter-drier combo.

    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Quote Originally Posted by desA View Post
    How sure are we of this, in practice though? Are there practical examples in the field where we can draw comparisons? Has anyone examples of a vertical filter-drier positioned at a level above the condenser outlet?
    The more common example would be the receiver inlet above the condenser outlet... and in fact this would seem to be the normal configuration for most smaller condensing units.

  38. #38
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    http://www.compactheatpumps.org/docs...flow_x_0.2.m1v

    http://www.compactheatpumps.org/docs...flow_x_0.2.m1v

    Take a look at the above videos of flow within compact plate heat-exchangers. You will observe that a fair amount of wavelike motion & thrashing about takes place in the flow streams. Add to this the interference from back-pressure, condensate levels etc & I'd believe that the dynamics will be anything short of smooth, uninterrupted flow.

    Take a look & think about it. Plate HE's are not the same at tube-in-tube systems, I'll bet
    Last edited by desA; 04-05-2010 at 06:09 PM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  39. #39
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Quote Originally Posted by Gary View Post
    The more common example would be the receiver inlet above the condenser outlet... and in fact this would seem to be the normal configuration for most smaller condensing units.
    If anyone has some pictures of this idea applied to PHE's, this would be useful.

    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  40. #40
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Puzzle

    Interesting videos, Des.

    The transition from liquid to vapor and vice versa might correctly be viewed as contained explosion/implosion. Nothing smooth about it.

  41. #41
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    I thought they were downright scary when I first saw them.

    I think that the compressor pulsations also have a lot to do with the flow instabilities. The pulsing swings back & forth at entrance/exits are something I've seen in flow simulations, with definite instabilities - a lot of whipping back & forth. The short contact length of these beasts makes for some very interesting system dynamics.

    I think there's a lot to still be learned about how these HE's operate. Very challenging.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  42. #42
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Now, take a look at the downward flow video, again. Concentrate on the liquid outflow through the small pipe.

    Now, imagine a certain amount of condensate filling the bottom of the PHE, then back it up a bit further, say due to back-pressure in the discharge line. Combine this further with bubbles of vapour trying to climb backwards back into the HE.

    What would the outlet nozzle flow dynamics & pressure drop be like? Could this lead to a 'blockage' situation, resulting from flow-induced phenomena alone?

    Perhaps under these conditions, oversizing of the discharge exit nozzle could be an advantage?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  43. #43
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Condenser Puzzle

    Quote Originally Posted by desA View Post

    What would the outlet nozzle flow dynamics & pressure drop be like? Could this lead to a 'blockage' situation, resulting from flow-induced phenomena alone?

    Perhaps under these conditions, oversizing of the discharge exit nozzle could be an advantage?
    Seems like your thinking along the same lines as I was, some fairly dynamic action and as the dynamic part slows it adds to the static pressure, but at the outlet of the plate the vena contractor may look like a restriction to flow and so a possible temp drop?

    The JT effect can be caused by a blockage or flow induced pressure drops.

    Chef

  44. #44
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Thanks very much, Chef.

    The PHE flow dynamics are fairly challenging.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  45. #45
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condenser Puzzle

    Hi DesA.
    Watched the videos, weird stuff going on inside PHEs. Hence the failure rate from internal failures from rapid and continual temp changes.
    I think the low pressure drop through PHEs has alot to do with the problems. I have had that opinion for years, and the videos confirm that.
    magoo

  46. #46
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Quote Originally Posted by Magoo View Post
    Hi DesA.
    Watched the videos, weird stuff going on inside PHEs. Hence the failure rate from internal failures from rapid and continual temp changes.
    I think the low pressure drop through PHEs has alot to do with the problems. I have had that opinion for years, and the videos confirm that.
    magoo
    PHE's are also very thin-walled. With pressure fluctuations, the units may very well fatigue over time.

    I wonder if some sort of inlet pulsation damper, or equaliser, to damp out the compressor pulsations, would help here?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  47. #47
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Condenser Puzzle

    Quote Originally Posted by Gary View Post
    Nope... no pilot receiver. Assume a simple water cooled A/C system with TXV.

    But if there were a pilot receiver, how could that cause the refrigerant exit temp to drop below the water inlet temp?
    Had a system where the pilot valve was stuck in a semi open state and when the compressor was on low capacity the refrigerant was evaporating almost all the way back to the condenser
    -Cheers-

    Tycho

  48. #48
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Condenser Puzzle

    So riddle me this and riddle me that - oh thats Batman. Off Topic.

    So are we closer to a real solution to this riddle?

  49. #49
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser Puzzle

    Quote Originally Posted by Chef View Post
    So are we closer to a real solution to this riddle?
    Hi Chef,
    I'm currently running charge trials on an equivalent system & am watching for similar behaviour, if any, to the raised exit filter-drier.

    I'll report back when sensible findings occur.

    The forward plan is to re-pipe the offending machine, & re-test that one, to see if a direct cause can be found. Still a work-in-progress, I'm afraid.

    Either way, this comparison can be used to benefit the greater public learning.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. Problem with plugged condenser
    By kurt s in forum Fundamentals
    Replies: 7
    Last Post: 02-10-2008, 06:46 PM
  4. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  5. Plate Heat Exchagers - Condenser
    By Billy Ray in forum Technical Discussions
    Replies: 9
    Last Post: 11-05-2008, 06:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •